ION meter configuration for 3W-Wye

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION meter configuration for 3W-Wye
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
RobGraham
Commander RobGraham Commander
Commander

Posted: ‎2024-12-18 03:08 AM

0 Likes
2
525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-18 03:08 AM

ION meter configuration for 3W-Wye

I am at a site where the wye transformers have been grounded through an HRG--no neutral is pulled back to the breakers or the meters.  When I arrived, the meters were configured as 3W-Wye, which seems to make sense. 

 

What caught my attention was that some meters had the nominal voltage set to the L-L nominal, and some L-N.  Those with L-L are capturing PQ events normally, while the L-L meters are not.  This seems to contradict the ION Reference:  

 

NOTE: Nominal refers to the primary power system RMS voltage (line-to-line
voltage for Delta systems and line-to-neutral voltage for Wye systems).

 

Furthermore, there are a couple of notes around the ION Reference suggesting 3W-Wye may ignore the V2 input, and FA244106 seems to state this meter should be set up as Delta:  How can the PowerLogic meters monitor a 3 wire ungrounded WYE system | Schneider Electric USA

 

My question is, for a meter monitoring a network through a wye transformer using an HRG and no ground bus, what should the wiring type be and what should I set the nominal voltage to?

 

Thanks for your help!

Labels
  • Labels:
  • ION8000
  • ION9000
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-12-18 07:35 AM

0 Likes
0
503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-18 07:35 AM

Hello @RobGraham 

3W-wye is not the volts mode you should be using. This is a very special configuration that is sometimes used in Utility type applications where a single CT to stepdown 100skV to 120V is worth more than the meter. In the install guide there is an image for the one and ONLY wiring that should be used with 3W-wye.

Charles_Murison_0-1734535880896.png


In your system, if the load is not connected to the same ground as the transformer to have a delta load, therefore I would suggest putting the meter into Delta mode. V nominal would be VL-L. If the load does have a ground connection, you will need to connect the same ground to the Vref(VN) of the meter. Volts mode would be 4W-wye and V nominal will be VL-N. 


Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-12-18 07:35 AM

0 Likes
0
504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-18 07:35 AM

Hello @RobGraham 

3W-wye is not the volts mode you should be using. This is a very special configuration that is sometimes used in Utility type applications where a single CT to stepdown 100skV to 120V is worth more than the meter. In the install guide there is an image for the one and ONLY wiring that should be used with 3W-wye.

Charles_Murison_0-1734535880896.png


In your system, if the load is not connected to the same ground as the transformer to have a delta load, therefore I would suggest putting the meter into Delta mode. V nominal would be VL-L. If the load does have a ground connection, you will need to connect the same ground to the Vref(VN) of the meter. Volts mode would be 4W-wye and V nominal will be VL-N. 


Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
RobGraham
Commander RobGraham Commander
Commander

Posted: ‎2024-12-18 08:57 AM

1 Like
0
497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-18 08:57 AM

Thank you very much for a comprehensive solution!  I missed the wiring in the installation guide, and now I can confidently tell customers, "Don't use this.".

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of