Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION Protocol / EtherGate - Third Party Gateway Hardware?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION Protocol / EtherGate - Third Party Gateway Hardware?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
JamesAZZO
JamesAZZO
Leader

Posted: ‎2014-04-06 10:12 PM

0 Likes
6
3741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-06 10:12 PM

ION Protocol / EtherGate - Third Party Gateway Hardware?

As you can see from this thread () - there are still those of us who have situations where we are using a number of ION protocol meters (timely with the PM8000 release next year) like the ION 7330/7350 and because of various reasons (like the inclusion of the analog I/O option cannot choose Ethernet as an optional card) we need to get these meters on Ethernet, but we need a direct protocol transmission with no transformation. (which is why the EGX-100 doesn't work). In Management Console in IONE/SPM/PME, there is a Gateway Port for Lantronix MSS, but those devices have been updated as noted.

I need to know if anyone is CURRENTLY using any of these new devices to achieve this functionality and any limitation they know of.

Looks like: Serial Ethernet Converter - External Device Servers - UDS1100 - Lantronix and Lantronix - UDS1100-IAP are options? although it's hard to see the difference?

We need a timely response from someone who has done this recently. or any ideas from what you guys have done? do you recall doing anything like this recently?

Tags (2)
  • Tags:
  • ethergate
  • ion
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
matt_azzo_com_a
matt_azzo_com_a
Contributor

Posted: ‎2014-04-23 10:34 PM

2 Likes
1
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-23 10:34 PM

To close the loop for all who might be interested, we got in one of these gateways (Serial Ethernet Converter - External Device Servers - UDS1100 - Lantronix) and can confirm that it meets our needs for communicating to meters using ION protocol.

Setup was simple, just entered the correct serial settings and changed the local port to 3001 (not necessary, but this matches the Lantronix option in the Configure Site settings in Management Console).

As James mentioned, this works well for occasions where we need ION protocol and Ethernet isn't an option, but as it can't do Modbus TCP/RTU conversion it's no replacement for the EGX-100.

See Answer In Context

Reply
Replies 6
matt_azzo_com_a
matt_azzo_com_a
Contributor

Posted: ‎2014-04-23 10:34 PM

2 Likes
1
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-23 10:34 PM

To close the loop for all who might be interested, we got in one of these gateways (Serial Ethernet Converter - External Device Servers - UDS1100 - Lantronix) and can confirm that it meets our needs for communicating to meters using ION protocol.

Setup was simple, just entered the correct serial settings and changed the local port to 3001 (not necessary, but this matches the Lantronix option in the Configure Site settings in Management Console).

As James mentioned, this works well for occasions where we need ION protocol and Ethernet isn't an option, but as it can't do Modbus TCP/RTU conversion it's no replacement for the EGX-100.

Reply
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2014-04-24 11:20 AM

1 Like
0
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-24 11:20 AM


Lantronix should have a variant of its gateway devices that does do Modbus TCP to RTU conversion.  At least years ago they did when we started to use modbus more extensively.  It is doubtful they will have all the extra features of the EGX line like SW logging etc as Lantronix just does plain TCP to serial conversion but they may be a good option for some applications.

Reply
sesa10844_bridg
sesa10844_bridg Contributor
Contributor

Posted: ‎2014-04-24 01:41 PM

1 Like
0
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-24 01:41 PM

We've used the following in the past:

  • Lantronix UDS1100-IAP
  • XPress-DR+
  • XPress-DR-IAP
  • XPress-DR

Most recently (purchased/installed mid-last year), we used the XPress-DR with ION protocol (7650 meters and 7500 RTUs).

Reply
Anonymous user
Not applicable

Posted: ‎2014-05-01 03:24 PM

1 Like
1
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-05-01 03:24 PM

Hi James,

We have successfully used the MOXA Nport 5150 and Nport 5232 in the past as an ION TCP/IP to serial gateway.  You just need to get the serial and TCP settings right.

Reply
Yut
Yut
Leader

Posted: ‎2014-07-18 01:22 AM

0 Likes
0
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-07-18 01:22 AM

In Thailand I always use the Wisco RC-33 Ethenet to RS-232/485/422 converter from www.wisco.co.th local products. Recently I install over 20 units of these converters around campus the biggest university in Thailand (installed every buildings to connect the PM820 at the building MDB via FO network).

Reply
arjanbijker
arjanbijker Leader
Leader

Posted: ‎2014-10-02 05:37 AM

0 Likes
0
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-10-02 05:37 AM

Hi Todd,

you can share the serial and TCP settings that worked for you?

Thanks

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore