ION 9000

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
XtianPilarcA
Lieutenant JG
Lieutenant JG
0 Likes
3
398

ION 9000

Hi, community.

 

Can somebody confirm if it’s possible to output the value of demand to the analog output module of the ION9000?

Our customer wants to confirm this before placing an order.

 

Thank you and Regards

Tags (1)

Accepted Solutions
Charles_Murison
Picard Picard
Picard

Re: ION 9000

Hello @XtianPilarcA ,

 

To the question, yes this can be done. The analog output module has a few setup registers that control how the input to the module affects the output as mentioned above. The one step not mentioned above is that the input to the analog output module needs to be linked to the desired Sliding window demand module's output. This can be done using ION Setup software. For more information on the analog output module refer to https://www.se.com/ca/en/download/document/7EN02-0290/.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
3 Replies 3
UdhayakumarAK
Lt. Commander Lt. Commander
Lt. Commander

Re: ION 9000

Hi

Whats the demand range will be set? i.e Zero scale value & Full Scale value to drive Analog Output.

Whats type of application will be used? i.e ION9K Analog output will be connected to Analog Input for which device

 

In general, ION9K Analog Output (kW output can be used as Analog output) supports for applications to drive control valves.

 

Thanks & regards

Udhayakumar.A.K

Tags (1)
Charles_Murison
Picard Picard
Picard

Re: ION 9000

Hello @XtianPilarcA ,

 

To the question, yes this can be done. The analog output module has a few setup registers that control how the input to the module affects the output as mentioned above. The one step not mentioned above is that the input to the analog output module needs to be linked to the desired Sliding window demand module's output. This can be done using ION Setup software. For more information on the analog output module refer to https://www.se.com/ca/en/download/document/7EN02-0290/.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
Yut
Captain
Captain

Re: ION 9000

To what system do you want to share data? If SCADA I recommend using standard protocol like MODBUS or  DNP 3 via meter communication ports. 

To use the Analog out port send demand value I can confirm that this ION9000 is capable you need to add something in the framework.

Tags (1)