Hi All,
We are having an issue trying to use the Lastest ION Setup to upgrade the firmware of a ION 9000 which has v2.0. We have tried upgrading it it version 2.1 first but it's coming up with the following.
There's a screen capture attached.
Anyone have any ideas what this could be?
It's not allowing the process to continue and asking for the meter to be Downgraded/Upgraded to v1.4?
Link copied. Please paste this link to share this article on your social media post.
By the looks of the log file, you are using the wrong IP port for standard ION communications:
8:59:57 AM: Software Version (Build): 3.2 (Build 21279)
9:00:08 AM: Incorrect password
9:00:08 AM: Upgrade started at Monday, 8 November 2021 9:00:08 AM
9:01:36 AM: Device Name = ion 9000 ut3
9:01:36 AM: Device Serial Number =
9:01:36 AM: Device IP Address = 10.22.142.8/502
502 is typically used for Modbus TCP, while ION is 7700.
10:12:53 AM: Software Version (Build): 3.2 (Build 21006)
10:12:53 AM: Upgrade started at Monday, 17 May 2021 10:12:53 AM
10:12:53 AM: Device Name = Meter1
10:12:53 AM: Device Serial Number = ME-1905B045-02
10:12:53 AM: Device IP Address = 192.168.99.12/7700
Link copied. Please paste this link to share this article on your social media post.
Could you possibly upload your UPGRADE.LOG file found in the C:\ProgramData\Schneider Electric\ION Setup folder.
Either ION Setup is unable to detect the firmware for the ION9000 or something is wrong with it reading the information from the upgrade file.
Link copied. Please paste this link to share this article on your social media post.
Hi There,
I've uploaded the file you requested.
The dates is from 8th Nov for that meter upload.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Hi - looks like device firmware and serial number are empty in the file. Per Rob's comment - can you confirm ut3 is communicating?
Link copied. Please paste this link to share this article on your social media post.
By the looks of the log file, you are using the wrong IP port for standard ION communications:
8:59:57 AM: Software Version (Build): 3.2 (Build 21279)
9:00:08 AM: Incorrect password
9:00:08 AM: Upgrade started at Monday, 8 November 2021 9:00:08 AM
9:01:36 AM: Device Name = ion 9000 ut3
9:01:36 AM: Device Serial Number =
9:01:36 AM: Device IP Address = 10.22.142.8/502
502 is typically used for Modbus TCP, while ION is 7700.
10:12:53 AM: Software Version (Build): 3.2 (Build 21006)
10:12:53 AM: Upgrade started at Monday, 17 May 2021 10:12:53 AM
10:12:53 AM: Device Name = Meter1
10:12:53 AM: Device Serial Number = ME-1905B045-02
10:12:53 AM: Device IP Address = 192.168.99.12/7700
Link copied. Please paste this link to share this article on your social media post.
Hello @bao_securebits_
Did changing the ports help with your upgrade?
Regards,
Charles