Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

ION 7650 password

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 7650 password
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
299
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
72
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
sesa241307
sesa241307 Cadet
Cadet

Posted: ‎2019-04-05 12:55 AM

0 Likes
9
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-05 12:55 AM

ION 7650 password

Hi am i able to reset or get a master password for ION7650 if forgoten of password?

 

I had 4 x ION7650 lock with password unable to edit or change any setting. 

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2019-04-05 08:14 AM

0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-05 08:14 AM

With enhancements to cybersecurity, there is no way to reset the password. The meters will need to be returned to the factory and reprogrammed. Any customization will be lost.

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 9
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2019-04-05 08:14 AM

0 Likes
0
1107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-05 08:14 AM

With enhancements to cybersecurity, there is no way to reset the password. The meters will need to be returned to the factory and reprogrammed. Any customization will be lost.

L4 Prime for Advanced metering and Utilities
Reply
Robert_Lee
Captain Robert_Lee Captain
Captain

Posted: ‎2019-04-05 09:03 AM

0 Likes
7
1103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-05 09:03 AM

If you used ION Setup Security Assistant wizard to program the password(s) AND you decided to save those settings to file at the completion of the wizard, then it may be possible for us to view the file and inform you of what the passwords were contained in that file (these are located in the C:\ProgramData\Schneider Electric\ION Setup\Security sub-folder).  Otherwise Charles is correct that cybersecurity features prevent any means to retrieve/reset the password of the ION7650 presently.

Reply
mustafap
Lieutenant JG mustafap
Lieutenant JG

Posted: ‎2023-03-13 12:40 AM . Last Modified: ‎2023-03-13 12:41 AM

0 Likes
6
456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-13 12:40 AM

Dear  @Robert_Lee ,

 

We have a similar problem at our customer, 2 of ION7650 are locked with password and no one now the passwords.

There are Encripted Security files at ProgramData file folder is it possible to view the passwords for us?

Where should we send the files ?

 

Thanks,

Reply
Robert_Lee
Captain Robert_Lee Captain
Captain

Posted: ‎2023-03-14 09:00 AM

0 Likes
0
445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-14 09:00 AM

I suggest contacting @Charles_Murison and provide either the 2 files themselves or the AuthenticationCode found within the file themselves (view the file using Notepad).

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-03-14 09:04 AM

0 Likes
4
443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-14 09:04 AM

Hello @mustafap,

 

I suggest you contact your local tech support team. If they are unable to help you, you can send me the case number and I can follow up with them.

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
mustafap
Lieutenant JG mustafap
Lieutenant JG

Posted: ‎2023-03-20 05:31 AM

0 Likes
3
423
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-20 05:31 AM

Dear @Charles_Murison 

 

Last week I contacted to Tech Support but the current responses didnt solved the problem.
the Ref number is as following;

RE: ION7650 Password [ ref:_00DA0abSm._5008V1XS1Ez:ref ]

 

Thanks for your help.

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-03-20 08:31 AM . Last Modified: ‎2023-03-20 09:11 AM

0 Likes
2
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-20 08:31 AM

Hello @mustafap ,

When programming the security with ION Setup, at the last step, a user is promoted with option to save the configuration to a file on the computer with extension of .scf. With this file and the help of support it is possible to recover the password. Without this file, if password is lost there is nothing I nor tech support can do. In the case I did not see any mention of a .scf file.

 

The only option is to return the meter to factory.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
mustafap
Lieutenant JG mustafap
Lieutenant JG

Posted: ‎2023-03-20 09:44 AM

0 Likes
1
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-20 09:44 AM

Dear @Charles_Murison 

 

I attached the scf files to a mail and send to support with the same Ref.

Can someone support for the recovery?

I can also attach here if you wish.

 

Thanks,

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-03-20 02:09 PM

0 Likes
0
408
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-20 02:09 PM

Hello @mustafap ,

 

Those .scf files are the default files that come with ION Setup, there is no customer details in those.

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc