Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM5320 meter KWH reading not matching with ION setup

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5320 meter KWH reading not matching with ION setup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Chiragshah
Chiragshah Explorer
Explorer

Posted: ‎2023-03-16 03:30 AM

0 Likes
4
3733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-16 03:30 AM

PM5320 meter KWH reading not matching with ION setup

Dear Team,

 

We have received one complaint for PM5320 meter. Issue observed is KWH reading mismatch . on meters display it is showing 5.665Gwh while on ion setup it is showing 1666949.887 kwh. So please confirm how to resolve it.

is there any limitation on ION setup to show maximum value?

all other parameters showing OK value.

 

Meter OS - 2.1.5

DOM - 5/22/22

Serial no - 540110068733

 

@Ramasamy_N 

Labels
  • Labels:
  • PM5000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2023-03-22 01:30 PM

0 Likes
0
3684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-22 01:30 PM

ION Setup is reading by default the INT64 register location (3204 onwards).  Please read those registers to see what are the contents.

See Answer In Context

Reply
Replies 4
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2023-03-16 04:29 AM

0 Likes
0
3728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-16 04:29 AM

Hello @Chiragshah 

There is no limitation in ION setup real time data view for the energy. 

Can you share the screen shot of ION setup energy page and the meter summary page? 

Also read and share the Modbus register values from 2700 (FLOAT32 format -12 registers).

 

Regards, 

Ramasamy N 

Reply
Chiragshah
Chiragshah Explorer
Explorer

Posted: ‎2023-03-22 12:03 AM

0 Likes
1
3705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-22 12:03 AM

Dear Ramasamy,

We have checked again with Modscan and ION setup. Meter display values are matching with Modscan but not matching with ION setup. only KVARh is matching in ION. Pls find attached screen shots.

 

@Ramasamy_N 

Attachments
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2023-03-22 07:28 AM . Last Modified: ‎2023-03-22 07:39 AM

0 Likes
0
3694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-22 07:28 AM

Thank you @Chiragshah for sharing the details, Please share the meter remote access details to Robert Lee for the analysis. 

 

Hello @robert.lee@se.com Can you please check this behavior? 

The ION setup real time energy values are not matching for 5GWh. 

 

Regards, 

Ramasamy N

 

 

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2023-03-22 01:30 PM

0 Likes
0
3684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-22 01:30 PM

ION Setup is reading by default the INT64 register location (3204 onwards).  Please read those registers to see what are the contents.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore