Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

ION 7500 battery life remaining value

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 7500 battery life remaining value
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
520
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
131
Ramasamy_N
Captain Ramasamy_N Captain
115
Robert_Lee
Admiral Robert_Lee Admiral
96
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
mark_BGIS
Ensign mark_BGIS
Ensign

Posted: ‎2022-09-27 08:22 AM

0 Likes
4
1833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-27 08:22 AM

ION 7500 battery life remaining value

Hello,

 

I have 2 ION 7500 meters that are connected via a serial to ethernet converter that I need to reset the battery life value. When I connect to the meter using ION Setup, I don't see the "Percent Battery Remaining" value.

 

I also tried to connect thru telnet, but after getting "connected", I just get a blank screen with a flashing cursor.

 

I was told that I can change the value through Designer, but was not told where to find the setting.

 

Does anyone how how to do this using Designer?

 

Thanks.

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2022-09-28 03:08 PM . Last Modified: ‎2022-09-28 03:22 PM

1 Like
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-28 03:08 PM

The ION7500 RS232 port is in DTE configuration and requires a NULL-modem adapter to connect to a standard PC's DCE RS232 port.

Of course the baud rate must also match the Com1 configuration settings. Press ENTER once or twice to see the prompt.

See the ION7500 installation manual for more information about the RS232 port.

 

I do not believe the 7500 (what firmware version do you have?) has the ability to reset the Battery life counter via ION (Designer) like the ION8650 has.

The ION7500 can have the battery counters reset (in the event you have replaced the battery with a new one) with the factory terminal command: BATCLEAR
and read the current state: BATSTAT

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 4
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-09-27 12:04 PM

0 Likes
2
1826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-27 12:04 PM

Hello @mark_BGIS ,

 

"I was told that I can change the value through Designer, but was not told where to find the setting." The person who told you this my have gotten this mixed up with other ION meters. For the ION7500 the battery life reset is done through terminal commands. Typical method to access terminal command is Telnet. However if you have Ethernet to serial gateway you will not be able to Telnet to the meters, Telnet connections would be telnet to the gateway itself. 

 

You might be able to connect to the meter serial port with a protocol of "Factory". You would need to use a terminal program such as Putty or Tera Term to connect to the serial port on your computer that is connected to the meter's serial port. Would need to have the serial settings match between meter and computer. If meter has only RS-485 serial port, would need to use a converter such as USB to RS-485.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
mark_BGIS
Ensign mark_BGIS
Ensign

Posted: ‎2022-09-27 01:17 PM

0 Likes
1
1823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-27 01:17 PM

Hello,

 

Thanks for the reply.  The meter does have an rs-232 port on it and I did try to connect to it that way initially.  I set the serial port protocol to "factory" and using both putty and Tera Term I opened a connection but all I get is a black screen with a flashing cursor in the top left corner and I can't type anything.

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-09-28 10:00 AM

0 Likes
0
1804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-28 10:00 AM

Hello Mark,

 

"Flashing cursor" could be any number of things. RS-232 port needs to have a number of setting on the meter hardware, (RS-485 vs RS-232) RTS/CTS Verses RTS + Delay, baud rate and serial settings parity stop bits etc. Not practical to try and troubleshoot over the forum. 

A good test is to confirm if you use ION protocol on serial port you can connect to the meter via ION Setup.

 

Note that when connecting to the meter you likely will need to hit "Enter" to get a response from the meter at first. Just connecting to the serial port will not generate any text on the console.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2022-09-28 03:08 PM . Last Modified: ‎2022-09-28 03:22 PM

1 Like
0
1794
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-28 03:08 PM

The ION7500 RS232 port is in DTE configuration and requires a NULL-modem adapter to connect to a standard PC's DCE RS232 port.

Of course the baud rate must also match the Com1 configuration settings. Press ENTER once or twice to see the prompt.

See the ION7500 installation manual for more information about the RS232 port.

 

I do not believe the 7500 (what firmware version do you have?) has the ability to reset the Battery life counter via ION (Designer) like the ION8650 has.

The ION7500 can have the battery counters reset (in the event you have replaced the battery with a new one) with the factory terminal command: BATCLEAR
and read the current state: BATSTAT

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore