ION 7350 reading Vll give 6553.6

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 7350 reading Vll give 6553.6
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
CiroF
CiroF
Cadet

Posted: ‎2024-05-18 01:01 PM

0 Likes
3
645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-18 01:01 PM

ION 7350 reading Vll give 6553.6

Hi

i have an old powerlogic 7350 meter.

concatenate voltage of the system is 11.000 V.

in the modbus map i can find concatenate in register 40015-18 and the readings need to be divided by 10.

The problem is that in a single uint16 you can't store more than 65536 (required 110.000) and infact i have 6553.6 voltage reading.

Am i missing something ? what is wrong ?

 

Regards

 

Ciro

Labels
  • Labels:
  • ION7000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-05-21 11:56 AM . Last Modified: ‎2024-05-21 11:59 AM

2 Likes
1
614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-21 11:56 AM

The ION7350 is a very old ION product but you have a number of available options to allow you to read the voltage.

1. The primary reason you need to divide the value by 10 is the factory default option is to allow 1 decimal point of resolution in Modbus register reads for voltage.  (i.e. If the voltage reading on the 7350 was 120.2 volts, the register would read 1202).  If you don't require this extra digit of resolution and want just the integer portion of voltage you can turn off the scaling via the Modbus Slave module setup register.  You would need to connect to the meter using ION Setup software and go into Advanced ION module view and set the MSR1 Scaling to No from Yes.

Robert_Lee_0-1716317623065.png

2. The second option would be if you do still want to support the extra decimal point of resolution (or maybe more) but can adjust the Modbus Master from reading UINT32 from UINT16 is to modify the MSR1 Format from the default Unsigned 16B to Unsigned 32B (this may require adjust all of the Modbus slave modules as this fundamentally alters the addressing in use).

The easiest option I recommend is to give up the extra digit of resolution.

Also keep in mind that making either adjustment will also affect all voltage/amps/freq readings unless you begin adjusting which readings to into which modules.  You could use the ION Setup Modbus Slave wizard to help in that regard and allow it to perform the necessary changes for you.




See Answer In Context

Reply
Replies 3
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-05-21 11:56 AM . Last Modified: ‎2024-05-21 11:59 AM

2 Likes
1
615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-21 11:56 AM

The ION7350 is a very old ION product but you have a number of available options to allow you to read the voltage.

1. The primary reason you need to divide the value by 10 is the factory default option is to allow 1 decimal point of resolution in Modbus register reads for voltage.  (i.e. If the voltage reading on the 7350 was 120.2 volts, the register would read 1202).  If you don't require this extra digit of resolution and want just the integer portion of voltage you can turn off the scaling via the Modbus Slave module setup register.  You would need to connect to the meter using ION Setup software and go into Advanced ION module view and set the MSR1 Scaling to No from Yes.

Robert_Lee_0-1716317623065.png

2. The second option would be if you do still want to support the extra decimal point of resolution (or maybe more) but can adjust the Modbus Master from reading UINT32 from UINT16 is to modify the MSR1 Format from the default Unsigned 16B to Unsigned 32B (this may require adjust all of the Modbus slave modules as this fundamentally alters the addressing in use).

The easiest option I recommend is to give up the extra digit of resolution.

Also keep in mind that making either adjustment will also affect all voltage/amps/freq readings unless you begin adjusting which readings to into which modules.  You could use the ION Setup Modbus Slave wizard to help in that regard and allow it to perform the necessary changes for you.




Reply
CiroF
CiroF
Cadet

Posted: ‎2024-05-23 12:14 AM

0 Likes
0
583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-23 12:14 AM

Hi Robert

And Many many many thanks for your answer.

 

So both solutions, require connection via modbus cable to the device.

I will try as soon as possible.

the plant is in England, and i am in Italy 🙂

 

but meanwhile does the device have already a modbus data area in which data are stored at 32bit ?

I downloaded the data map but it seems that "extended" data map is available only for other devices 75xx and 76xx not 73xx.

 

Regards 

 

Ciro

 

Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-05-23 01:08 PM

1 Like
0
576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-23 01:08 PM

No the extended data map may exist for the 73xx but certainly does not include 32 bit versions of existing data.  Unlike most fixed Modbus maps, the ION devices back then allowed users to configure their own map however they wanted.  Also since this product is over 20+ years old 32 bit registers were not supported as well as they are today.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of