ION 7330 through Ethertgate "ION7400" can not connect

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 7330 through Ethertgate "ION7400" can not connect
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
525
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
138
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
PowerLogic
PowerLogic ION7400 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
JuanMQT
Lieutenant JG JuanMQT
Lieutenant JG

Posted: ‎2021-06-24 11:24 AM . Last Modified: ‎2024-01-30 04:42 AM

0 Likes
3
2306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-24 11:24 AM

ION 7330 through Ethertgate "ION7400" can not connect

Dear experts,

 

I have a costumer who wants to communicate his ION7330 through a ION7400 to a PME, its ION7330 has an ethernet port that is being used to report to a SCADA, acording to the manual the ION7330 supports a single Ethernet connection at a time. That's why we are trying through a gateway.

But I can not connect with the ION7330 

 

ION7330

ION7330 Baud rate.jpegION7330 ID.jpegION7330 Protocol.jpegION7330 Serial.jpeg

 

ION7400

ION7440 Gateway.jpegION7400.PNG

 

What should I do ?

  • Thumbnail of PowerLogic ION7400 series
    PowerLogic
    PowerLogic ION7400 series
View products (1)
Labels
  • Labels:
  • ION7000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2021-09-08 03:09 PM . Last Modified: ‎2021-09-08 03:43 PM

1 Like
0
2286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-08 03:09 PM

Does the ION7330 have a Modem installed (RJ-11 on the side of the unit).  If so, the Com1 RS-485 can only be used as an outgoing ModemGate port (allowing any communication via incoming modem calls to also talk to downstream devices) and can not be used to communicate to the device itself from the RS-485 side.  The Com2 port is also reserved for outgoing Ethergate operation if the meter is installed with Ethernet which you've indicated is being used by SCADA.

Unfortunately this only leaves the front optical port as the only means to communicate to the device if you can't use the modem to dial into the 7330 without disconnecting SCADA.

Another limited alternative would be to use the ION7400 to Modbus Master via TCP the ION7330 which would allow both SCADA and PME to connect to the ION7400 (since it supports multiple simultaneous connection and not just one like the 7330) but this limits the type of data retrieved to a limited set of real-time data.

If the unit does NOT have a modem port, then you should be able to communicate to the 7330 by using ION Setup, adding a gateway site using the ION7400 IP address and IP Port 7801, then adding an ION 7330 device to that site with a unit ID of 10.  Keep in mind that again only 1 software can connect to the Ethergate port so if ION Setup is connected, PME will not be able to at the same time.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 3
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-09-08 09:31 AM

0 Likes
0
2299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-08 09:31 AM

Hello @JuanMQT ,

 

I moved this post to the hardware forum. The settings and wiring look correct. Could try turning off the RS485 bias but I would not hold my breath that will fix the issue. Do you see activity lights on the ION7330 when you try to read? What software are you using to try connect with ION7330?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2021-09-08 10:46 AM

0 Likes
0
2293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-08 10:46 AM

Are you trying to connect via ION Setup or PME?  Is there any additional diagnostic information you are seeing (connection to ION7400 is ok, but serial timeouts to 7330?)

Tags (1)
  • Tags:
  • english
Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2021-09-08 03:09 PM . Last Modified: ‎2021-09-08 03:43 PM

1 Like
0
2287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-08 03:09 PM

Does the ION7330 have a Modem installed (RJ-11 on the side of the unit).  If so, the Com1 RS-485 can only be used as an outgoing ModemGate port (allowing any communication via incoming modem calls to also talk to downstream devices) and can not be used to communicate to the device itself from the RS-485 side.  The Com2 port is also reserved for outgoing Ethergate operation if the meter is installed with Ethernet which you've indicated is being used by SCADA.

Unfortunately this only leaves the front optical port as the only means to communicate to the device if you can't use the modem to dial into the 7330 without disconnecting SCADA.

Another limited alternative would be to use the ION7400 to Modbus Master via TCP the ION7330 which would allow both SCADA and PME to connect to the ION7400 (since it supports multiple simultaneous connection and not just one like the 7330) but this limits the type of data retrieved to a limited set of real-time data.

If the unit does NOT have a modem port, then you should be able to communicate to the 7330 by using ION Setup, adding a gateway site using the ION7400 IP address and IP Port 7801, then adding an ION 7330 device to that site with a unit ID of 10.  Keep in mind that again only 1 software can connect to the Ethergate port so if ION Setup is connected, PME will not be able to at the same time.

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore