Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Communication response of PM5000 energy consumption

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Communication response of PM5000 energy consumption
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Miyai
Miyai
Contributor

Posted: ‎2021-09-08 10:50 PM

0 Likes
7
2971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-08 10:50 PM

Communication response of PM5000 energy consumption

Hello,

 

Please let me know how the PM5000 response will be.

 

 

The maximum energy value of PM5000 is 9,223,372,036,854,775,807.

The energy value is stored in a signed 64 bit integer register (INT64).

 

Please let me know the response of the communication to the above.

(1) For the Float32 type of Modbus register 2700, the maximum value is 2^24=16,777,215.

What response is returned when this value is exceeded?

 (ex. 16,777,215→0→1→2, or N/A or ???)

 

(2) For the INT64 type of Modbus register 3204, the maximum value is 9,223,372,036,854,775,807. Is the response in this case 16,777,215→16,777,216→….→9,223,372,036,854,775,807→0?

 

 

Best regards,

Miyai

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2021-09-09 11:50 PM

0 Likes
5
2955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-09 11:50 PM

Hello @Charles_Murison  @Miyai 

 

The PM5000 series meter energy value will get reset to 0 when it reached to the max value 9,223,372,036,854,775,807 ( max value of INT64). 

The max value of FLOAT32 format is higher than the INT64 max value ( 3.4028235 × 1038  ). It is not direct like INT32 or INT64. 

So we have limited the max energy value in PM5000 series to the max value of INT64. 

 

Regards,

Ramasamy N

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-09-09 03:03 PM

0 Likes
6
2964
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-09 03:03 PM

Hello @Ramasamy_N ,

 

Do you know what modbus values the meter will give for the different conditions?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2021-09-09 11:50 PM

0 Likes
5
2955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-09 11:50 PM

Hello @Charles_Murison  @Miyai 

 

The PM5000 series meter energy value will get reset to 0 when it reached to the max value 9,223,372,036,854,775,807 ( max value of INT64). 

The max value of FLOAT32 format is higher than the INT64 max value ( 3.4028235 × 1038  ). It is not direct like INT32 or INT64. 

So we have limited the max energy value in PM5000 series to the max value of INT64. 

 

Regards,

Ramasamy N

Tags (1)
  • Tags:
  • english
Reply
Miyai
Miyai
Contributor

Posted: ‎2021-09-13 02:02 AM

0 Likes
4
2938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-13 02:02 AM

Hell @Ramasamy_N 

 

I thought the maximum value of Float32 was 16,777,215 (=2^24-1). based on the following URL.

 

https://www.proface.com/support/index?page=content&country=APS_GLOBAL&lang=en&locale=en_US&id=FA2391...

 

 


Is this understanding wrong?

Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2021-09-13 02:17 AM

0 Likes
0
2936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-13 02:17 AM

Hi @Miyai 

 

This FAQ is not applicable for PM5000 series meter. 

The maximum value of FLOAT32 is  3.4028235 × 1038

Which is high value than INT64, So we are resetting the energy values when it reached to max value of INT64.
 
Regards,
Ramasamy N
Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-09-13 08:53 AM

0 Likes
2
2931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-13 08:53 AM

Hello @Miyai ,

 

I key phrase in the KB you linked is " without loss of resolution on the stored number."

 

In float 32, a number is represented as (sign)*(2^exp)*(precision) encoded into 32 bits. 1 bit is used for sign, either 1 or -1, exp is 8 bits and precision is 24 bits. The exp can range from −126 to 127. The precision I think is where you are getting the number 16,777,215 from. This is the largest number that you can get before every whole number is not possible to represent using this format (loss of resolution). This is why many meters recommend using 10,000,000 as the roll over value, it is an easy number for humans to understand and below the ~16.777 million. 

 

While the exp is still small (~24) the most difference you would see is 1 between the desired number and what is represented in the float output, however when the exp gets larger, the gaps between each possible number gets bigger and bigger.  

 

A tool that could possibly help you visualize this is https://www.h-schmidt.net/FloatConverter/IEEE754.html

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
DanL
DanL Champion
Champion

Posted: ‎2021-09-13 09:51 AM . Last Modified: ‎2021-09-13 09:56 AM

0 Likes
1
2926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-13 09:51 AM

The important context with precision is that with the float32 numeric format (see https://en.wikipedia.org/wiki/Single-precision_floating-point_format) there are always (at least) 7 digits of decimal precision for all working values.

For example, a kWh output register, output values will appear to increment by 0.001 at 16,778kWh, 0.1 at 1,677,722kWh, and 100 at 1677,721,500kWh.

Tags (1)
  • Tags:
  • english
Reply
Miyai
Miyai
Contributor

Posted: ‎2021-09-13 09:22 PM

0 Likes
0
2915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-13 09:22 PM

Hello @DanL , @Charles_Murison , @Ramasamy_N 

 

Thank you for your advice.

I understood.

 

 

Best regards,

Miyai

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore