Hi all,
We have this ION 7300 meter at one of customer sites. We are trying to integrate this into the building automation via modbus but the meter screen has a message "No Screens Programmed" and meter readings are coming out null on the modbus.
Anyone has a fix for this?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hi @Akash
Please note that ION7300 series meters are obsolete and are no longer supported.
Since both Display and Modbus are not functioning, I am wondering if meter's Template has been changed/manipulated. If you check meter in Advanced mode of ION Setup(hold control key and select the meter), by default meter has 1-8 Display Modules and 1-4 Modbus Slave Modules linked to different parameters:
If Modules do not exist or their links have been changed incorrectly, I would recommend uploading the default Template again to the meter to see if meter displays the default parameters and responds to Modbus polls of default Modbus registers.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @Akash
Please note that ION7300 series meters are obsolete and are no longer supported.
Since both Display and Modbus are not functioning, I am wondering if meter's Template has been changed/manipulated. If you check meter in Advanced mode of ION Setup(hold control key and select the meter), by default meter has 1-8 Display Modules and 1-4 Modbus Slave Modules linked to different parameters:
If Modules do not exist or their links have been changed incorrectly, I would recommend uploading the default Template again to the meter to see if meter displays the default parameters and responds to Modbus polls of default Modbus registers.
Best Regards,
-Mehran
L3 Expert Advanced metering