Continue
  • My Subscriptions
  • Events
My Values for Voltage, Current, and Power Factor are correct, but Power is low
Metering & Power Quality
  • EcoStruxure Power & Grid
  • My Values for Voltage, Current, and Power Factor are correct, but Power is low
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
MikeChan
MikeChan
Explorer
Posted: ‎2024-10-11 04:35 PM
2023
Hi Everyone,
I would like to understand the solution for a low power reading issue. My calculations indicate approximately 1.8 MW, but the meter is showing around 0.633 MW, resulting in low energy readings.
Thanks in advance
  • PM8000
Tags (2)
  • pm8240
Mehran_Mehrnia
Champion
Posted: ‎2024-10-14 01:16 PM
Hi @MikeChan
It's very likely that the Phase Order(ABC or ACB) or VT, CT polarities are not correct. You could check and verify this by looking at Phasor Viewer tool using ION Setup:
There is an option to temporarily change Polarity Settings when selecting 'Show Setup' button(image above already selected changed to 'Hide Setup') in case the polarity in the field is not correct.
Best Regards,
-Mehran
L3 Expert Advanced metering
Mehran_Mehrnia
Champion
Hi @MikeChan
Best Regards,
-Mehran
Charles_Murison
Champion
Posted: ‎2024-10-15 09:33 AM
Hello @MikeChan ,
Having the total power being ~1/3 of the expected power would strongly suggest that 1 phase is reversed. Getting voltage and current phase angles would be a good first step. If you cannot get that, then a per phase power and signed power factor reading could also help.
Charles