ION 7300 Modbus TCP - Voltages Reading Problem

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 7300 Modbus TCP - Voltages Reading Problem
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
OnurGurhan
Ensign OnurGurhan Ensign
Ensign

Posted: ‎2016-08-04 06:23 AM . Last Modified: ‎2020-04-22 01:22 AM

1 Like
5
1582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-04 06:23 AM

ION 7300 Modbus TCP - Voltages Reading Problem

Hi Everyony;

I can not read Voltage registers via Modbus TCP from ION 7300.

40011,40012,40013 register values are always 65535.

 

I wanna check modbus registers and firmware of 7300 so Im trying to connect ION setup via serial but i could not.(7300s are at the field has no Ethernet.)

How can i connect it ? Do you have any configuration ?

 

PS: I choose ION protocol, 9600 baud from device while trying to conncet ION setup

Labels
  • Labels:
  • ION Setup
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2016-08-04 07:04 PM

0 Likes
0
1515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-04 07:04 PM

One thing to keep in mind is the ION73xx series of devices only allow a single connection to certain IP ports if using Ethernet (so if PME is already connected to the device via Ethernet, ION Setup would be unable to connect at the same time).

Also some of the serial ports are out-going connections *IF* the meter is equipped with either Ethernet (COM2) or a Modem (COM1).  The serial port is used to allow the meter to operate as a gateway to other devices so can no longer be used to communicate to the actual meter.

Ideally, you could use a ANSI optical probe to communicate via the front optical, or if the meter does have Ethernet, either connect using a direct cross-over cable or make sure to disable any other connections like PME or other software to allow ION Setup to connect to the device via TCP.  If you are attempting to communicate using the COM1 RS-485 port, you can also switch to view Comm diagnostics on the front panel to see if the meter is receiving and/or transmitting information (if your RS-485 converter is working properly).  You should also make sure ION Setup is using No Parity/8 data bits/1 stop bit for comm settings as that is the only settings the ION73xx meters support.

Reply
Yut
Captain Yut
Captain

Posted: ‎2016-08-17 10:56 PM

1 Like
2
1515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-17 10:56 PM

If you use serial port using ION Setup be sure to set timing, RTS and CTS both must be Disable whether connect via RS-485 port or optical port.

Reply
OnurGurhan
Ensign OnurGurhan Ensign
Ensign

Posted: ‎2016-08-26 12:27 AM

0 Likes
1
1515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-26 12:27 AM

I think the error occurs because of PT Pri/Sec config.

PT Pri/Sec arraged as 34500/100. So we can see the 32300 Volt at the meter screen.

Voltage registers for 7300 are defined Unsigned16 so 32000 volts are over ranged for Unsigned 16 and sends 65530(over range value)

When i configured PT as 3450/100, i can read 3230 volt from these registers.. no problem.

In my opinion, it would fixed if I can convert it to "kV" at display or meter config.

How can i make it 32,3 kV ?? Its easy to make at 7650 but couldnt find it at 7300

Thanks in advance

Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2016-09-20 12:04 PM

1 Like
0
1516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-09-20 12:04 PM

One possible solution is to scale the Modbus Slave modules for voltages by setting the In Scaling larger than the Out Scaling (you will lose resolution and you would have to interpret the values on the Modbus side by multiplying the values back out.

Ex. 32303 would scale down by 10 to 3230 which is the value you would read via Modbus and then you would scale it back out by multiplying by 10 to 32300.

Another alternative would be to switch to 32 bit registers (either INT or UINT) depending on whether your master is capable of interpreting those formats.

Reply
OnurGurhan
Ensign OnurGurhan Ensign
Ensign

Posted: ‎2016-10-06 01:14 AM

0 Likes
0
1516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-06 01:14 AM

I created new registers for voltages. I defined them 32 registers except of 16 unS. and FAILED

The problem is still continus. I think new register reads value from real voltage signal. (16 bit unS)

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of