New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
IFM communication module failure
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2017-02-0912:53 AM
IFM communication module failure
Hello,
Has anyone encountered multiple IFM modules failure?
We have a customer with 16 IFM modules on 4 different switchboards that have stopped communicating with PME. Client is concerned with the reliability of these modules as they have about 250 of these modules. We tested by replacing the offline IFMs with functional IFMs from spare breakers in the same switchboard.
Upon further investigation, we found that the faulty IFMs stopped communicating after a power outage as the main ION7350 meter reported a loss of power.
The IFM modules are connected to ION7350 meter as gateway.
SWB A - 2 of 4 IFM faulty
SWB B - 4 of 9 IFM faulty
SWB C - 5 of 21 IFM faulty
SWB D - 4 of 21 IFM faulty
There are another 3 IFMs comms on 2 different switchboards that went offline recently and we are yet to test but ION7350 again reported power loss the time the IFM went offline.