IEM 3255 Not giving consistent pf values.

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • IEM 3255 Not giving consistent pf values.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
488
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Sabyasachi
Sabyasachi
Cadet

Posted: ‎2024-06-19 04:20 AM . Last Modified: ‎2024-06-19 04:21 AM

0 Likes
2
693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-19 04:20 AM

IEM 3255 Not giving consistent pf values.

Hi All,

I am facing an issue with reading the RS485 data with the IEM 3255 Energy meter.

When I am trying to see the pf from the meter screen itself, it's showing me as -0.84 as shown in the image.Meter screenMeter screen

However, when I'm trying to read from RS485 Bus, particularly, I am reading the register 0x0C0B, I am getting a response as " BF 8D 6F DA ". 

This value, which is in IEEE754 floating point format, If I convert, I'm getting as ' -1.1049759 '. 

 

Can anybody help me out with this problem?

The meter is connected in 3P3W configuration, all CT ratios are correct and even wiring type is correct.

Labels
  • Labels:
  • iEM3000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-06-19 10:33 AM

0 Likes
0
664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-19 10:33 AM

Hi @Sabyasachi 

 

As Charles mentioned correctly, iEM3000 series the same as PM5500 series perform a simple algorithm to the PF value then stores it in the PF register.
iEM3000 Power factor register format

Thank you.

Best Regards,

-Mehran

L3 Expert Tech Support Specialist

See Answer In Context

Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-06-19 10:21 AM

0 Likes
0
672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-19 10:21 AM

Hello @Sabyasachi 


I believe the link below is for the PM5500 series but I believe the format is the same
https://www.productinfo.schneider-electric.com/pm5500/595e2aa946e0fb0001f715da/PM5500%20User%20Manua...

The PF value is calculated from the PF register value using the following formulas:

Quadrant PF range PF register range PF formula

Quadrant 1

0 to +1

0 to +1

PF value = PF register value

Quadrant 2

-1 to 0

-2 to -1

PF value = (-2) - (PF register value)

Quadrant 3

0 to -1

-1 to 0

PF value = PF register value

Quadrant 4

+1 to 0

+1 to +2

PF value = (+2) - (PF register value)

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-06-19 10:33 AM

0 Likes
0
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-19 10:33 AM

Hi @Sabyasachi 

 

As Charles mentioned correctly, iEM3000 series the same as PM5500 series perform a simple algorithm to the PF value then stores it in the PF register.
iEM3000 Power factor register format

Thank you.

Best Regards,

-Mehran

L3 Expert Tech Support Specialist

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of