Abon
Waveform captures can be accessed using ION Setup software.
Status:
Select the appropriate option to enable or disable this feature.
File Mode:
Select which method is used for storing waveforms:
“FIFO” (first-in-first-out) mode discards the oldest waveform capture when the waveform storage is full.
“Fill and Hold” mode keeps the oldest waveform capture and does not record new ones when the waveform storage becomes full.
Channels (PM870 only)
This allows you to select which inputs you want to set up for waveform capture.
Select “Channels” then click Edit.
Depending on your wiring configuration, certain inputs become N/A (not applicable). If this is the case, ION Setup displays this prompt:
1. Select the voltage and/or current input channels you want to capture. Click Next.
2. Set the capture options:
Samples/Cycle
Duration (cycles)
Pre-Event Cycles
Max Capture indicates the maximum number of recordings for waveform capture, and is shown for informational purpose only.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Abon
Waveform captures can be accessed using ION Setup software.
Status:
Select the appropriate option to enable or disable this feature.
File Mode:
Select which method is used for storing waveforms:
“FIFO” (first-in-first-out) mode discards the oldest waveform capture when the waveform storage is full.
“Fill and Hold” mode keeps the oldest waveform capture and does not record new ones when the waveform storage becomes full.
Channels (PM870 only)
This allows you to select which inputs you want to set up for waveform capture.
Select “Channels” then click Edit.
Depending on your wiring configuration, certain inputs become N/A (not applicable). If this is the case, ION Setup displays this prompt:
1. Select the voltage and/or current input channels you want to capture. Click Next.
2. Set the capture options:
Samples/Cycle
Duration (cycles)
Pre-Event Cycles
Max Capture indicates the maximum number of recordings for waveform capture, and is shown for informational purpose only.

Posted: 2013-10-22 04:55 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Barry,
Thanks for your reply.
I'm thinking about writing a script to implement what you suggested with IONSetup and get captured waveform file( JPEG?) in a specific directory that BMS can access.
Sent from mobile
"Barry Cantrell" <powersolutionscommunity-admin@powersolutionscommunity.hosted.jivesoftware.com> 於 2013/10/23 0:10 寫道:
Solutions Expert Community
How to get PM870 waveform w/o PME software?
reply from Barry Cantrell in Power Monitoring Hardware - View the full discussion
Abon
Waveform captures can be accessed using ION Setup software.
Status:
Select the appropriate option to enable or disable this feature.
File Mode:
Select which method is used for storing waveforms:
“FIFO” (first-in-first-out) mode discards the oldest waveform capture when the waveform storage is full.
“Fill and Hold” mode keeps the oldest waveform capture and does not record new ones when the waveform storage becomes full.
Channels (PM870 only)
This allows you to select which inputs you want to set up for waveform capture.
Select “Channels” then click Edit.
Depending on your wiring configuration, certain inputs become N/A (not applicable). If this is the case, ION Setup displays this prompt:
1. Select the voltage and/or current input channels you want to capture. Click Next.
2. Set the capture options:
Samples/Cycle
Duration (cycles)
Pre-Event Cycles
Max Capture indicates the maximum number of recordings for waveform capture, and is shown for informational purpose only.
Reply to this message by replying to this email, or go to the message on Solutions Expert Community
Start a new discussion in Power Monitoring Hardware by email or at Solutions Expert Community
Following How to get PM870 waveform w/o PME software? in these streams: Inbox
>
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Abon,
Please keep us updated with how you go with this, I have a customer who is interested in a similar solution. They want to use our meters but refuse to use SPME.
I'm also keen to understand if it will be possible to access the sag/swell/transient waveforms via the same method?
Regards,
Steven Yan
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Abon -
I'll be interested in what you learn when you investigate the waveform display function of ION Setup. I don't know how this is done, but I guess that it reads the Modbus registers in the meter and then maps/displays the data. I do know that we have not publicly released the meter's Modbus mapping of the waveforms.
Regards,
John Straughn
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
hi all,
are there any news? I am also interessted in this captured waveform file.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.