Dear All
is there anyone know how to disable PQ Alarm on PM870 ?
because i do it via ION Setup but it isn't successfull
i have been disable it and send the setting to the meter,
but when i check again, it still active
is anyone can help me ?
Link copied. Please paste this link to share this article on your social media post.
Please not that PM800 series are obsolete and are not officially supported.
The PQ Alarm on the PM870 not disabling via ION Setup is likely due to the EN50160 Evaluation feature being enabled. When this feature is active, it reserves certain alarm positions for its own use, preventing manual changes, even if you send the settings to the meter.
So, please make sure EN50160 is disabled.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Please not that PM800 series are obsolete and are not officially supported.
The PQ Alarm on the PM870 not disabling via ION Setup is likely due to the EN50160 Evaluation feature being enabled. When this feature is active, it reserves certain alarm positions for its own use, preventing manual changes, even if you send the settings to the meter.
So, please make sure EN50160 is disabled.
Best Regards,
-Mehran
L3 Expert Advanced metering