How to connect to an ION7550 directly using iON setup3.0
Metering & Power Quality
  • EcoStruxure Power & Grid
  • Re: How to connect to an ION7550 directly using iON setup3.0
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
202
Ramasamy_N
Ramasamy_N Champion
115
sesa287810
sesa287810 Leader
Leader
Posted: ‎2015-02-16 04:54 PM
1202
I have connected an iON7550 using a usb-rs485 converter directly to my laptop. I have tried to connect this one meter as a single device and I have tried to connect as a network. I want to capture the historic voltage highs in a meter.
I have tried to connect via an EGX100 with both iON setup and PME and cannot communicate with the meter at all. I have the meter set to protocol Modbus RTU @ 19200 and 8N1. I have tried changing the protocol to iON and still does not connect. Note there is no Ethernet port on this meter. I can however read holding registers using a Modbus scanner with both serial and Ethernet/gateway connections. Why will it not work with PME or iON setup??
sesa186702
sesa186702 Leader
Leader
Posted: ‎2015-02-17 07:11 AM
Dear Chantal Farrelly,
For your case, You should change the protocol of Serial port  to ION protocol to connect direct it to IONSetup or PME
IONSetup just support ION protocol for direct connect...Otherwise (Modbus protocol), you just can use EGX Gateway to connect it
Best Regard
Reply 1
sesa186702
sesa186702 Leader
Leader
Best Regard