Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
HI Everyone
I am reading ION8650 Data using IEC61850.
If NTP and SNTP time synchronization is performed on the ION8650, is there any work that needs to be done separately?
Or is it done if I set NTP and SNTP in Advanced Ethernet in the ION Setup I know?
If I need to set it in .CID and other places, I wonder how to proceed.
Regards
JungRyeol
Link copied. Please paste this link to share this article on your social media post.
Hello @jryang_SAM-A ,
IEC61850 does not make any communication changes to the meter via the CID file. Any communication settings need to be programmed onto the meter via ION either ION Setup or Power Monitoring Expert Designer or front panel.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @jryang_SAM-A ,
IEC61850 does not make any communication changes to the meter via the CID file. Any communication settings need to be programmed onto the meter via ION either ION Setup or Power Monitoring Expert Designer or front panel.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.