How to Delete the ION7650 Event Log

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • How to Delete the ION7650 Event Log
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
jryang_SAM-A
Lieutenant | EcoXpert Master jryang_SAM-A Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2018-01-17 08:50 PM

0 Likes
5
1436
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-01-17 08:50 PM

How to Delete the ION7650 Event Log

Hello everyone?

This is the current time synchronization setting.
You can confirm that the event log records the time synchronization as shown in the picture every day.
KakaoTalk_20180118_134011099.jpg
Time Synchronization Event Log makes it difficult to find other Event Logs.

Is there a way to turn off only the time synchronization event log?

Thank you.

Tags (4)
  • Tags:
  • event log
  • ion 7650
  • ntp
  • time sync
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Yut
Captain Yut
Captain

Posted: ‎2018-01-17 10:04 PM

0 Likes
2
1360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-01-17 10:04 PM

Your time sync. occurred  quite too often. I recommend you to study the clock module setting concern NTP.

NTP Time Sync Interval

This register specifies the frequency at which the meter will attempt to time

synchronize via SNTP. Values between 60 seconds and 1 year are acceptable.

NTP Event Logging Threshold

This register specifies the minimum time synchronization difference (in seconds)

for a time synchronization event to be logged. This value is only used for NTP time

synchronization.

This would minimize number of events caused by NTP time sync. but not to eliminate time sync. at all sometime you need this event for problem solving hope this may help.

Reply
jryang_SAM-A
Lieutenant | EcoXpert Master jryang_SAM-A Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2018-01-17 11:13 PM

0 Likes
1
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-01-17 11:13 PM

Hi Yut Kijasanong

I know this.

However, there is a problem because the time synchronization period is changed when the threshold value is changed.

We will ask you if you can prevent the event log from being recorded.

Regardes

Reply
Yut
Captain Yut
Captain

Posted: ‎2018-01-21 07:55 PM

0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-01-21 07:55 PM

One more, try to look for NTP time change priority no. see if you can set cutoff at the event controller.

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2018-01-22 09:16 AM

0 Likes
1
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-01-22 09:16 AM

One other option could be to change the clock seeing from using the line frequency to the internal clock. Could help keep the meter from needing as many time sync.

L4 Prime for Advanced metering and Utilities
Reply
Anonymous user
Not applicable

Posted: ‎2018-03-05 11:36 PM

0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-05 11:36 PM

Is there anything we can do within the meters framework so it's not logging (or displaying) every event?

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of