Hi Everyone,
I have a question about BCPM split-core type CT amp ratings.
I have a project that has many 250A branch circuits. BCPMSC E-type meters would be suitable for a few of their panels . Except that according to the BCPM datasheet, split core branch CTs are only available up to 200A. However the specifications for the split-core branch CT and split-core main auxiliary CT seem to be the same - 0.333V output.
BCPMSCCT3 200A split-core 1.8m lead
LVCT00302S 300A split-core 0.333V output
Thus, my question is, can I use the 300A split-core CT (LVCT00302S) on my BCPM branch circuits?
Link copied. Please paste this link to share this article on your social media post.
Unfortunately, the branch input are using current mode CTs and not LVCT. So you cannot do this substitution.
I will check what we can offer to meet your needs.
Link copied. Please paste this link to share this article on your social media post.
Hi Arnaud,
This project we are working on has 5 panels that have multiple branch cirucits requirements.
22, 14, 14 ,8, 21 branches, (3-phase 380V, 100 ~250A)
Please let me know if you have any suggestions.