Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How does the ION meter keep time when the power is off?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • How does the ION meter keep time when the power is off?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
T.Okada
T.Okada
Contributor

Posted: ‎2021-12-14 03:04 AM

0 Likes
6
2222
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-14 03:04 AM

How does the ION meter keep time when the power is off?

Hi support,

 

Our customer asked me " How does the ION meter keep time when the power is off? " 

and "Is it possible to replace the battery if the ION meter keeps time using something like coin battery?"

if so, how often do they have to replace it?

 

Do you have any idea?

 

Thanks,

Okada

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-12-14 10:10 AM

0 Likes
5
2214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-14 10:10 AM

Hello @T.Okada ,

 

I moved your question to the metering forum. For the first question "How does the ION meter keep time when the power is off?" This is done with a battery that is used to power the meter's clock. 

 

As for your next question, there are some details missing such as what type and version of ION Meter. 

 

For example, ION7650 meters have 2 different versions, the most common is the Comm Card has a socket where a battery can be placed. See https://www.se.com/in/en/faqs/FA411084/ for more details.

 

ION8650 meters have a detachable battery that can be replaced. See here 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 6
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-12-14 10:10 AM

0 Likes
5
2214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-14 10:10 AM

Hello @T.Okada ,

 

I moved your question to the metering forum. For the first question "How does the ION meter keep time when the power is off?" This is done with a battery that is used to power the meter's clock. 

 

As for your next question, there are some details missing such as what type and version of ION Meter. 

 

For example, ION7650 meters have 2 different versions, the most common is the Comm Card has a socket where a battery can be placed. See https://www.se.com/in/en/faqs/FA411084/ for more details.

 

ION8650 meters have a detachable battery that can be replaced. See here 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
T.Okada
T.Okada
Contributor

Posted: ‎2021-12-14 04:13 PM

0 Likes
2
2207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-14 04:13 PM

Hi Charles,

 

Thank you for answering my question quickly!

and sorry for lack of meter type information.

 

In this case, our customer uses METSEION92040 and METSEPM8240.

 

Would you please tell me about these models?

 

Thanks,

Okada

 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-12-14 04:47 PM . Last Modified: ‎2021-12-15 10:24 AM

0 Likes
1
2205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-14 04:47 PM

Hello @T.Okada ,

 

The ION9000 and PM8000 meters have a battery with expected lifespan of at least 7 years. The battery replacement kit has not yet been commercialized. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
T.Okada
T.Okada
Contributor

Posted: ‎2021-12-14 05:35 PM

0 Likes
0
2200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-14 05:35 PM

Hi Charles,

 

Thank you for your support.

 

I understand about the battery of ION9000 and PM8240.

 

Best regards,

Okada

 

 

Tags (1)
  • Tags:
  • english
Reply
galcaPsE
galcaPsE
Explorer

Posted: ‎2023-01-31 05:58 PM

0 Likes
1
1891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-31 05:58 PM

Hello @Charles_Murison and @T.Okada,

I had an event where an ION8650A was turned off for 2 hours, then turned on and the clock was 4 minutes lag. It currently has a remaining battery percentage of 70% and the battery was replaced 6 years ago.

 

When the battery is new should theoretically keep time?

Is it time to change the internal battery?

 

I will appreciate your clarification,

 

Regards,

 

Gustavo

 

 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-02-01 08:38 AM

0 Likes
0
1884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-01 08:38 AM

Hello @galcaPsE ,

 

When the battery was replaced, were the counters reset to return to 100%? Not enough information to go on clock. Recommend you contact your local technical support and collect diagnostic information.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore