High Speed Data Recording with ION 8650 B

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • High Speed Data Recording with ION 8650 B
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
danielbarrantes
Lieutenant JG danielbarrantes
Lieutenant JG

Posted: ‎2024-05-15 08:50 AM

0 Likes
4
1043
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-15 08:50 AM

High Speed Data Recording with ION 8650 B

Hello, I have previously performed high speed measurements with an ION 7650 and with an ION9000, however, currently a client needs to perform these measurements with an ION8650 model B and I have a question if this model has this capacity and what would be the highest capacity. sampling? I mention this because I know that the ION8650 A and the ION 8650 B have different capacities and compliance with standards such as 61000-4-30 for example.

 

@Charles_Murison @Ricardo_RM 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-05-15 10:54 AM

0 Likes
0
1037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-15 10:54 AM

Hello @danielbarrantes ,

 

Can the ION8650 meter support high speed logging of high speed data? It depends. For a period of time yes. As a long term continuous logging, NO, the flash memory on the meter would ware away or data would get lost when meter is waiting to write to flash. 

Shorter periods of time, yes it may be possible, how many measurements logging for how long are some details that may play a factor.

The meter's data recorders share RAM memory and different configurations can use more or less of this shared memory.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-05-28 12:18 PM

1 Like
0
953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-28 12:18 PM

Hello @danielbarrantes ,

 

I have not personally tried to read high speed data through DNP on ION9000 meters but it looks like meter can be configured for high speed module operation.

 

A note about the following comments. ION meters like ION9000, PM8000, ION7400, as well as older meters will prioritize communication as a low priority task. Communication response rates can therefore never be guaranteed. With that being said, the DNP export module can be configured as a high speed module, this will use up a significate about of CPU so unlikely to have the full default DNP map as high speed. Each DNP salve export module has a maximum of 4 inputs. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 4
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-05-15 10:54 AM

0 Likes
0
1038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-15 10:54 AM

Hello @danielbarrantes ,

 

Can the ION8650 meter support high speed logging of high speed data? It depends. For a period of time yes. As a long term continuous logging, NO, the flash memory on the meter would ware away or data would get lost when meter is waiting to write to flash. 

Shorter periods of time, yes it may be possible, how many measurements logging for how long are some details that may play a factor.

The meter's data recorders share RAM memory and different configurations can use more or less of this shared memory.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
danielbarrantes
Lieutenant JG danielbarrantes
Lieutenant JG

Posted: ‎2024-05-15 11:04 AM

0 Likes
0
1034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-15 11:04 AM

Thank you very much for you response @Charles_Murison. My doubt was clarified.

 

 

Reply
danielbarrantes
Lieutenant JG danielbarrantes
Lieutenant JG

Posted: ‎2024-05-27 10:28 AM

0 Likes
1
969
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-27 10:28 AM


Hello, as part of this project, I am evaluating implementing an ION9000 so that it can send data through the high-speed modules to a SCADA. Previously we have successfully tested high-speed modules with sampling rates of up to 100ms from ION Setup and storing it in the internal memory of the meter, however, I would like to know if it is possible to send that data to a SCADA, via DNP3, with the same sampling rate (100 ms). Thank you. @Charles_Murison 

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-05-28 12:18 PM

1 Like
0
954
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-28 12:18 PM

Hello @danielbarrantes ,

 

I have not personally tried to read high speed data through DNP on ION9000 meters but it looks like meter can be configured for high speed module operation.

 

A note about the following comments. ION meters like ION9000, PM8000, ION7400, as well as older meters will prioritize communication as a low priority task. Communication response rates can therefore never be guaranteed. With that being said, the DNP export module can be configured as a high speed module, this will use up a significate about of CPU so unlikely to have the full default DNP map as high speed. Each DNP salve export module has a maximum of 4 inputs. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of