Continue
  • My Subscriptions
  • Events
【HDPM6000】For measurement of current only
Metering & Power Quality
  • EcoStruxure Power & Grid
  • 【HDPM6000】For measurement of current only
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
Miyai
Miyai
Contributor
Posted: ‎2024-07-02 11:27 PM
1438
Is there any way to measure current with the HDPM6000 with no voltage applied?
I am looking to measure only current circuits with HDPM6000 to replace BCPM C type.
However, we are looking for a solution because current values cannot be measured when no voltage is applied.
Is there a part to set up on the web browser?
Miyai
  • HDPM6000
Mehran_Mehrnia
Champion
Posted: ‎2024-07-03 08:01 AM
1412
Hi @Miyai
As mentioned in HDPM6000 Installation Guide the HDPM6000 head unit includes three separate electrical components that must be connected in order to use the system:
voltage reference, power supply and CTs.
Best Regards,
-Mehran
L3 Tech Support Specialist
Mehran_Mehrnia
Champion
1412
Hi @Miyai
Best Regards,
-Mehran
Miyai
Miyai
Contributor
Posted: ‎2024-07-03 10:44 PM
Hi @Mehran_Mehrnia
Thanks for the advice.
We suggest that the customer apply V1 voltage when replacing the BCPM type C.
Best regards,
Miyai
Mehran_Mehrnia
Champion
Posted: ‎2024-07-04 08:56 AM
Hi @Miyai
You're welcome.
Please note that unlike PCPM, if only V1 voltage is applied to the HDPM6000, the meter will solely measure and calculate parameters for phase 1 until V2 and V3 are applied to obtain parameters for the other phases.
Best Regards,
-Mehran
L3 Expert Tech Support Specialist