Why should HDPM6000 not be used for corner-grounded delta systems?
The manual says it can be applied if it is for ungrounded delta. The manual states that the wiring for phase B at that time should be connected to the N terminal.
I need advice as to why this is not applicable to corner-grounded delta systems.
Miyai
  • HDPM6000
Mehran_Mehrnia
Champion
Posted: ‎2024-07-03 01:51 PM
Hi @Miyai
As per design, and as mentioned in Installation Guide, HDPM6000 head unit is capable of measuring the voltage for the following Supply Types:
Delta 3-Wire ungrounded
Delta High-Leg
4-wire Wye
3-wire Split-phase
HDPM6000 may not have the necessary algorithms or hardware to accurately and safely handle the unique characteristics of corner-grounded delta systems.
Best Regards,
-Mehran
L3 Expert Tech Support Specialist
Mehran_Mehrnia
Champion
Hi @Miyai
Delta High-Leg
4-wire Wye
3-wire Split-phase
Best Regards,
-Mehran