Dear
I tried to put an over and under frequency alarm on a PM8x0 with ION Setup but frequency is neither in the over nor in the under alarm list.
With PMCU or SMS this isn't a problem......
Even when you put the alarm via PMCU or SMS and you return to ION setup your alarm is gone.....
I use IION Setup Version 3.0.13080.01. Is there may be a newer version?
Link copied. Please paste this link to share this article on your social media post.
Hi Jeroen,
Sorry but this seems to of been an oversight on my part. You can manually add the support by modifying the REGISTER.MAP file yourself using Notepad by following these instructions.
1. Using Notepad, open the REGISTER.MAP file found in one of the PM8x0 sub-folders in the sub-folder TABLES\SQD800 (ex. C:\Program Files\Schneider Electric\ION Setup\Tables\SQD800\PM870\REGISTER.MAP)
2. Find the ;1s Metering - Frequency line in the file (see below)
;1s Metering - Frequency
Reg41180=Frequency,FUINT16,NR1,S100,O0
3. Add to the end of the Reg41180= line so it looks like:
Reg41180=Frequency,FUINT16,NR1,S100,O0,0x0009
4. Save the file and open the Alarms setup screen again. Frequency should now be available for both Over and Under options.
I will try and get this change incorporated for all the CM/PM driver files for the next build I put on Box/FTP.
Link copied. Please paste this link to share this article on your social media post.
still not possible to put an frequency alarm on PM800 via ION Setup (Used Version 3.0.13214.01)
Link copied. Please paste this link to share this article on your social media post.
Hi Jeroen,
Sorry but this seems to of been an oversight on my part. You can manually add the support by modifying the REGISTER.MAP file yourself using Notepad by following these instructions.
1. Using Notepad, open the REGISTER.MAP file found in one of the PM8x0 sub-folders in the sub-folder TABLES\SQD800 (ex. C:\Program Files\Schneider Electric\ION Setup\Tables\SQD800\PM870\REGISTER.MAP)
2. Find the ;1s Metering - Frequency line in the file (see below)
;1s Metering - Frequency
Reg41180=Frequency,FUINT16,NR1,S100,O0
3. Add to the end of the Reg41180= line so it looks like:
Reg41180=Frequency,FUINT16,NR1,S100,O0,0x0009
4. Save the file and open the Alarms setup screen again. Frequency should now be available for both Over and Under options.
I will try and get this change incorporated for all the CM/PM driver files for the next build I put on Box/FTP.
Link copied. Please paste this link to share this article on your social media post.
Thanks....