Floating point of em6400++ integration into workstation
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2024-10-0402:10 PM
Hello Azo,
Not sure what specific workstation you are referring to. Typically, modbus clients are programmed to process modus responses and convert to the desired format. Usually the main consideration is the word order, high bytes first or last. 21 43 or 43 21.
Link copied. Please paste this link to share this article on your social media post.
2024-10-0402:10 PM
Hello Azo,
Not sure what specific workstation you are referring to. Typically, modbus clients are programmed to process modus responses and convert to the desired format. Usually the main consideration is the word order, high bytes first or last. 21 43 or 43 21.