PM8000 Failed Firmware Update

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Failed Firmware Update
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
526
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
138
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
mjr5097
Crewman mjr5097
Crewman

Posted: ‎2024-08-23 10:26 AM

0 Likes
3
1222
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-23 10:26 AM

PM8000 Failed Firmware Update

Hello,

I was updating the firmware on a PM8000 device and got a message saying "meter communication issue".  ION Setup then crashed.  The display now fails to connect to the meter and I can't reach the device on ION Setup.  

Here are the installation logs.  Any help would be appreciated!  

 

9:37:20 AM: Software Version (Build): 3.2 (Build 23305)

9:37:48 AM: Processing file: PM8000_V004.005.000.upx

9:37:48 AM: Upgrade started at Friday, August 23, 2024 9:37:48 AM

9:37:48 AM: Device Name = 78-1R

9:37:48 AM: Device Serial Number = ME-2110A177-02

9:37:48 AM: Device IP Address = xx/7700

9:37:48 AM: Device IPv6 Link Local = fe80::260:78ff:fe11:6f2c

9:37:48 AM: Device Firmware = 003.000.000

9:37:48 AM: Upgrade Power Cycles = 0

9:37:48 AM: Upgrade Filename: PM8000_V004.005.000.upx

9:37:48 AM: SHA256: 1617EEB9B2675A3C0721275B58AB9126B1A32D1303CC5BCA6D46D53FE85CA581

9:37:48 AM: Proceeding with firmware download

9:37:48 AM: Transmit delay: 0 ms

9:37:50 AM: Decreasing transmit delay: 0 ms

9:38:06 AM: 10% completed

9:38:06 AM: Comm efficiency = 100.0%

9:38:22 AM: 20% completed

9:38:22 AM: Comm efficiency = 100.0%

9:38:39 AM: 30% completed

9:38:39 AM: Comm efficiency = 100.0%

9:38:55 AM: 40% completed

9:38:55 AM: Comm efficiency = 100.0%

9:39:13 AM: 50% completed

9:39:13 AM: Comm efficiency = 100.0%

9:39:31 AM: 60% completed

9:39:31 AM: Comm efficiency = 100.0%

9:39:48 AM: 70% completed

9:39:48 AM: Comm efficiency = 100.0%

9:40:05 AM: 80% completed

9:40:05 AM: Comm efficiency = 100.0%

9:40:24 AM: 90% completed

9:40:24 AM: Comm efficiency = 100.0%

9:40:41 AM: 100% completed

9:40:41 AM: Comm efficiency = 100.0%

9:40:41 AM: Finalizing upgrade transfer

9:41:17 AM: Installing firmware: 10%

9:41:21 AM: Installing firmware: 20%

9:41:25 AM: Installing firmware: 30%

9:41:29 AM: Installing firmware: 40%

9:41:34 AM: Installing firmware: 50%

9:41:35 AM: Installing firmware: 60%

9:41:43 AM: Installing firmware: 70%

9:41:52 AM: Installing firmware: 80%

9:42:01 AM: Installing firmware: 90%

9:42:20 AM: Installing firmware: 100%

9:42:40 AM: Firmware installed successfully

9:42:40 AM: Device restarting...

9:42:40 AM: Disconnecting ethernet connection

9:42:40 AM: Ethernet connection disconnected

9:43:40 AM: Attempting to reconnect ethernet connection

9:43:40 AM: Ethernet connection reconnected: []

9:43:41 AM: Upgrade Power Cycles = 1

9:43:42 AM: Upgrade completed at Friday, August 23, 2024 9:43:42 AM

9:43:42 AM: Processing file: PM8000_webpages_V004.005.000.zip

9:43:42 AM: Web update started at Friday, August 23, 2024 9:43:42 AM

9:45:01 AM: Upgrade completed at Friday, August 23, 2024 9:45:01 AM

9:45:01 AM: Restoring framework C:\Users\xxx\Desktop\Config Files\78-1R.dcf

Labels
  • Labels:
  • ION Setup
  • PM8000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mjr5097
Crewman mjr5097
Crewman

Posted: ‎2024-10-07 04:26 AM

0 Likes
0
1069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-07 04:26 AM

The LED indicator is flashing red/green.  Meter is being replaced.

See Answer In Context

Reply
Replies 3
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
Admiral

Posted: ‎2024-08-29 11:47 AM . Last Modified: ‎2024-08-29 11:49 AM

1 Like
0
1212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-29 11:47 AM

Hi @mjr5097 

 

It seems the upgrade process is almost done except restoring Framework as I do not see 'Framework restored successfully' statement at the end of the Upgrade log.

 

Did you power cycle the meter and see if it can be reached?
Meter has the Status/Power LED, please check if it is solid green after power cycle or flashing Red/Green.

 

If it is flashing Red/Green, means startup or firmware upgrade sequence is in progress or likely meter is stuck in the boot loop. In this case, when there is no communication with the meter, unfortunately the only option is replacing the meter.

 

Best Regards,

-Mehran

L3 Expert tech Support Specialist

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-10-04 02:15 PM

0 Likes
0
1088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-04 02:15 PM

Hello @mjr5097 ,

 

Any follow up on this topic?

 

Were you able to paste the template?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
mjr5097
Crewman mjr5097
Crewman

Posted: ‎2024-10-07 04:26 AM

0 Likes
0
1070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-07 04:26 AM

The LED indicator is flashing red/green.  Meter is being replaced.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore