For IEM3000 series, the wire spec is also available from meter user guide. See screenshot below.
Link copied. Please paste this link to share this article on your social media post.
Hi Joseph
In the PM5100 install guide is mentioned the following cable:
RS-485 : Belden 3105A / Belden 3106A
http://download.schneider-electric.com/files?p_File_Id=745436274&p_File_Name=HRB32897-04.pdf
Here is the link to the cable:
http://www.belden.com/resourcecenter/tools/cablefinder/upload/18-2_5.pdf
The cable that you attached seems fine with this part of the recommendation:
+, -, , C 0.33 - 3.31 mm 2 (22 - 12 AWG)