Ask our Experts
Didn't find what you are looking for? Ask our experts!
Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2015-03-25 01:29 AM
Link copied. Please paste this link to share this article on your social media post.
For IEM3000 series, the wire spec is also available from meter user guide. See screenshot below.
Link copied. Please paste this link to share this article on your social media post.
Hi Joseph
In the PM5100 install guide is mentioned the following cable:
RS-485 : Belden 3105A / Belden 3106A
http://download.schneider-electric.com/files?p_File_Id=745436274&p_File_Name=HRB32897-04.pdf
Here is the link to the cable:
http://www.belden.com/resourcecenter/tools/cablefinder/upload/18-2_5.pdf
The cable that you attached seems fine with this part of the recommendation:
+, -, , C 0.33 - 3.31 mm 2 (22 - 12 AWG)
Posted: 2015-03-25 01:29 AM
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.