Does Schneider Electric recommend a particular RS485 cable 3 wire for use with IEM3000 and PM5000 series meters?

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
sesa70550_bridg
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
2
405

Does Schneider Electric recommend a particular RS485 cable 3 wire for use with IEM3000 and PM5000 series meters?

I have a customer asking if the attached cable would suffice given that it is an 3 wire DMX cable.

Attachments

Accepted Solutions
sesa237142_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
338

Re: Does Schneider Electric recommend a particular RS485 cable 3 wire for use with IEM3000 and PM5000 series meters?

For IEM3000 series, the wire spec is also available from meter user guide. See screenshot below.

6051

See Answer In Context

2 Replies 2
EduardoFainblum
Commander Commander
Commander
0 Likes
0
338

Re: Does Schneider Electric recommend a particular RS485 cable 3 wire for use with IEM3000 and PM5000 series meters?

Hi Joseph

In the PM5100 install guide is mentioned the following cable:

RS-485 : Belden 3105A / Belden 3106A

http://download.schneider-electric.com/files?p_File_Id=745436274&p_File_Name=HRB32897-04.pdf

Here is the link to the cable:

http://www.belden.com/resourcecenter/tools/cablefinder/upload/18-2_5.pdf

The cable that you attached seems fine with this part of the recommendation:

+, -, , C 0.33 - 3.31 mm 2 (22 - 12 AWG)

sesa237142_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
339

Re: Does Schneider Electric recommend a particular RS485 cable 3 wire for use with IEM3000 and PM5000 series meters?

For IEM3000 series, the wire spec is also available from meter user guide. See screenshot below.

6051