Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

Detail relating to IEC61000-4-30 ION modules

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Detail relating to IEC61000-4-30 ION modules
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
292
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
71
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
richard_schwass
Lt. Commander | EcoXpert Master richard_schwass Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2018-04-29 07:05 PM

1 Like
5
896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-04-29 07:05 PM

Detail relating to IEC61000-4-30 ION modules

Hi there,

We are beginning to work with a customer to develop frameworks around the early warning diagnosis of feeder faults. This will center around monitoring of high-speed rolling voltages, currents and harmonics.

It is clear to me that the 4-30 parameters which update 150/180 cycles could be best to use. Therefore theHarmonics Measurement and Power Quality Aggregator modules will get us started.

1. How do each of the four aggregation methods work in the Harmonics Measurement module?

    • Tvs Aggregation
    • Tvs Maximums
    • 4-30 150/180 Cycle
    • 4-30 10 Minute

2. What does Tvs stand for?

3. Is the 4-30 standards aggregation method an 'average'?

3. Which setting will give a 150/180 rolling average?

4. Which setting will give a 10 minute rolling average?

Kind regards

Richard

Tags (3)
  • Tags:
  • harmonics
  • iec 61000-4-30
  • ion7650
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2018-05-08 02:44 PM

0 Likes
0
837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-05-08 02:44 PM

Dan Loewen​

Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2018-05-08 04:36 PM

1 Like
2
837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-05-08 04:36 PM

1. How do each of the four aggregation methods work in the Harmonics Measurement module?

    • Tvs Aggregation
      • Allows for arbitrary time intervals of RMS aggregation of the 150/180 values. For example, If you needed distortion values at 1-minute intervals, you would pulse the Evaluate input every minute and get the RMS of all the 150/180 intervals in each minute.
    • Tvs Maximums
      • Allows for arbitrary time intervals of maximum reporting of the 150/180 values. For example, If you needed max 150/180 distortion values over each 10 minutes, you would pulse the Evaluate input every 10 minutes and get the peak of all the 150/180 intervals in each 10 minutes.
    • 4-30 150/180 Cycle
      • The is the strict Class A aggregation specified in IEC61000-4-30. It is always comprised of the rms of fifteen 10/12Cycle basic intervals.
    • 4-30 10 Minute
      • The is the strict Class A aggregation specified in IEC61000-4-30. It is always comprised of the rms of every (typically 3000 of them) 10/12Cycle basic intervals in a 10minute interval.

2. What does Tvs stand for?

     Tvs stands for "time very-short". It is a legacy term for 150/180 cycle (3s) interval predating IEC61000-4-30.

3. Is the 4-30 standards aggregation method an 'average'?

     The 4-30 time aggregation of magnitudes is always an RMS (root-mean-square). For a constant signal, the result is the same as average. I believe RMS was chosen because it is proportional to thermal effects from fluctuating harmonics (where an average would under register the severity)

3. Which setting will give a 150/180 rolling average?

     The "4-30 150/180 Cycle" method provides a non-overlapping rms approximately every 3 seconds.

4. Which setting will give a 10 minute rolling average?

     The "4-30 10minute" method provides a non-overlapping rms every 10 minutes.

Reply
richard_schwass
Lt. Commander | EcoXpert Master richard_schwass Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2018-05-08 06:08 PM

1 Like
1
837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-05-08 06:08 PM

Thanks Dan,

Perfect answers!

We should get this detail added to the ION Reference manual...

Eric Tjiptadjaja​, Arneil Dalope​, Leah Sun​

Cheers Richard

Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2018-05-09 09:13 AM

0 Likes
0
837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-05-09 09:13 AM

Matthew Curry​

Reply
GrahamSpencer
Lieutenant JG GrahamSpencer Lieutenant JG
Lieutenant JG

Posted: ‎2018-05-11 02:45 PM

0 Likes
0
837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-05-11 02:45 PM

Hi Richard, I assume your application is for feeder cables where you could have insulation failure that develops over some time, allowing possible detection by monitoring the parameters for small changes?

thanks

Graham

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.