Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Derating - ACcuSine PCS+

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Derating - ACcuSine PCS+
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
PowerLogic
AccuSine PCS+

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
SESA214337
SESA214337 Explorer
Explorer

Posted: ‎2023-05-16 03:17 AM

1 Like
2
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-16 03:17 AM

Derating - ACcuSine PCS+

Dear All, 

 

Last time when I check the event log of PCS+ 300A and found that:

1/The fault " Low Order Harm Disable" occurred many times.

2/Continue checking we found that there is very high temperature of IGBT L1: 83 Celsius degrees while others are L2: 65, L3: 48 degrees.

3/And the PCS+ derating to 80%  so total output very limit with 54/ 300A only.

 

So I don't know what is the root course of this issue and how to fix it.

Thank Team very much to advice.

  • Thumbnail of AccuSine PCS+
    PowerLogic
    AccuSine PCS+
View products (1)
Attachments
Labels
  • Labels:
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Arunprasad
Arunprasad Mentor
Mentor

Posted: ‎2023-05-16 05:00 AM

4 Likes
1
3428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-16 05:00 AM

Hello Vinh NGUYEN,

Here below are my feedback.

For Q-1- For each harmonic order a  limit is define. When this limit is reach  , Active filter will generate
 a  “limit action” for this harmonic. It means when the current of a harmonic order exceeds  the limit set point the harmonic order is disabled.  If harmonics  H5& H7 are disable by the action limit  , a message low 

harmonic will be  display. Most of time this means there is capacitor bank downstream to the active filter CTs .

 

For Q-2- Possible reason for the temperature raise can be due to improper air flow which could be caused due to dust accumulation inside the IGBT heat sinks if the units were not maintained properly.  Check for the Air flow from the top of the heat sink,  I think cleaning the IGBT heat fins might be a possible containment action. Check whether the blowers are working fine.

Due to air flow pattern at the intake side of the heat sink plenum L1 IGBT tends to collect dirt fastest so it will be the first heat sink to clog in a dirty environment.

But still i am not much happy with the temperature difference between L1 IGBT  L2 IGBT & L2 IGBT.

Unfortunately, the only way to be certain is to remove the heat sinks.  So i recommend to remove all the 3-nos of heat sink and try to clean out the heat sink with compressed air, capture some images before and after cleaning for our references.

Then after re-assemble the heat sinks relaunch the Integrity test for 15min.

Please capture the temperature at beginning of test , after 15min that is at the end of the test .

I hope after cleaning the heat sink the L1 IGBT temperature should be normal like other phase IGBT's.

 

For Q-3- I could see the Inlet Temperature measure 42 deg C is bit high, normally when the IGBT temperature get increased above it set point, Unit will get de-rate, so follow my suggestion that i provided for Q2, that will resolve this issue. Ensure the Site environment is good, it means a proper Ventilation was set for our AHF to have proper Air flow.

 

Please raise a BFO Case in CCC, we don't use this forum to discuss  more in detail.

 

Note: After following all the above process, if still you have any question, i recommend you to raise a BFO case through your country "CCC" team, Customer Care Center. Here below attached the link in both English and Vietnamese.

English

https://www.se.com/vn/en/work/support/customer-care/contact-schneider-electric.jsp

 

Vietnamese

https://www.se.com/vn/vi/work/support/customer-care/contact-schneider-electric.jsp

 

As i mentioned if you still have any question and if you have any concerns , Please approach us through BFO with below details

a) Product Commercial  reference - Image capture

b) Unit Serial number. 

c) Event log file

e) If you had RED Flag, press it and then capture the event that display in the HMI.

f) How long this unit was working in the customer site

g) What is the kind of environment is our AHF installed.

h) Single line diagram.( It need to capture the CT position's and the load's details).

i) Nature of load connected to AHF, Do all the non-linear load are installed with 3% line reactor.

j) Do any capacitor bank located at the downstream of the AHF.

 

Regards

 

Arunprasad

See Answer In Context

Reply
Replies 2
Arunprasad
Arunprasad Mentor
Mentor

Posted: ‎2023-05-16 05:00 AM

4 Likes
1
3428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-16 05:00 AM

Hello Vinh NGUYEN,

Here below are my feedback.

For Q-1- For each harmonic order a  limit is define. When this limit is reach  , Active filter will generate
 a  “limit action” for this harmonic. It means when the current of a harmonic order exceeds  the limit set point the harmonic order is disabled.  If harmonics  H5& H7 are disable by the action limit  , a message low 

harmonic will be  display. Most of time this means there is capacitor bank downstream to the active filter CTs .

 

For Q-2- Possible reason for the temperature raise can be due to improper air flow which could be caused due to dust accumulation inside the IGBT heat sinks if the units were not maintained properly.  Check for the Air flow from the top of the heat sink,  I think cleaning the IGBT heat fins might be a possible containment action. Check whether the blowers are working fine.

Due to air flow pattern at the intake side of the heat sink plenum L1 IGBT tends to collect dirt fastest so it will be the first heat sink to clog in a dirty environment.

But still i am not much happy with the temperature difference between L1 IGBT  L2 IGBT & L2 IGBT.

Unfortunately, the only way to be certain is to remove the heat sinks.  So i recommend to remove all the 3-nos of heat sink and try to clean out the heat sink with compressed air, capture some images before and after cleaning for our references.

Then after re-assemble the heat sinks relaunch the Integrity test for 15min.

Please capture the temperature at beginning of test , after 15min that is at the end of the test .

I hope after cleaning the heat sink the L1 IGBT temperature should be normal like other phase IGBT's.

 

For Q-3- I could see the Inlet Temperature measure 42 deg C is bit high, normally when the IGBT temperature get increased above it set point, Unit will get de-rate, so follow my suggestion that i provided for Q2, that will resolve this issue. Ensure the Site environment is good, it means a proper Ventilation was set for our AHF to have proper Air flow.

 

Please raise a BFO Case in CCC, we don't use this forum to discuss  more in detail.

 

Note: After following all the above process, if still you have any question, i recommend you to raise a BFO case through your country "CCC" team, Customer Care Center. Here below attached the link in both English and Vietnamese.

English

https://www.se.com/vn/en/work/support/customer-care/contact-schneider-electric.jsp

 

Vietnamese

https://www.se.com/vn/vi/work/support/customer-care/contact-schneider-electric.jsp

 

As i mentioned if you still have any question and if you have any concerns , Please approach us through BFO with below details

a) Product Commercial  reference - Image capture

b) Unit Serial number. 

c) Event log file

e) If you had RED Flag, press it and then capture the event that display in the HMI.

f) How long this unit was working in the customer site

g) What is the kind of environment is our AHF installed.

h) Single line diagram.( It need to capture the CT position's and the load's details).

i) Nature of load connected to AHF, Do all the non-linear load are installed with 3% line reactor.

j) Do any capacitor bank located at the downstream of the AHF.

 

Regards

 

Arunprasad
Reply
SESA214337
SESA214337 Explorer
Explorer

Posted: ‎2023-05-16 06:39 AM

0 Likes
0
3422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-16 06:39 AM

Dear Arunprasad,

 

Thank you for your advice.

I create case on the Bfo and send the question to CCC Team

Best regards.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore