Varplus logic with 3rd party capacitors

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Varplus logic with 3rd party capacitors
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2023-05-20 09:18 AM . Last Modified: ‎2023-05-20 09:19 AM

1 Like
2
733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-20 09:18 AM

Varplus logic with 3rd party capacitors

Hi All,

 

As we know one of the key features of the Varplus logic is to measure the remaining capacity of capacitors.

 SESA648446_0-1684599170489.png

 Based on the information shown in the above slide, I have two questions.

  • It seems that this feature is still working even with 3rd party capacitors?
  • Can the Varplus logic be used as a tool in a brownfield to measure the remaining capacity of the capacitors (both SE and 3rd party)? Kind of service helps customers determine when to replace the old capacitors. 

Thanks

Labels
  • Labels:
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
RavindraKulkarni
Ensign RavindraKulkarni Ensign
Ensign

Posted: ‎2023-05-22 02:19 AM

0 Likes
0
714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-22 02:19 AM

Hello,

 

This feature( remaining capacity) will work for third party capacitors also. The purpose of this function is to make the customer aware of the remaining capacity. There is also an alarm SPL/NR alarm which is generated when the step value falls below 75% of the original capacity. Once this alarm is generated for a step that step is converted to Fix OFF. It's recommended to replace the capacitor when this alarm is generated.

Reply
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2023-05-22 08:40 AM

0 Likes
0
710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-22 08:40 AM

Hi @RavindraKulkarni 

 

Thanks for your information.

 

From the slide I showed above, Varplus Logic will evaluate dQ (just before – just after) every time a step is switched, so I guess we can use Varplus Logic in a brownfield project (which currently does not have SE APFR) to measure the remaining capacity of the old capacitors. Am I correct in that? Thanks

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of