Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hi everyone,
Im trying to save data with a PM5560. I need Log all parameters of THD. I Download ION SETUP 3.0 and when I configure Datalogs, only appear Currents, Powers, Energy, Voltages, Power Factor, but no appear THD. Is possible Log this data?
Thanks for all!
Regards
Link copied. Please paste this link to share this article on your social media post.
ION Setup allows all the selection of parameters allowed by the PM55xx firmware. It is fairly easy to add additional registers in ION Setup but the firmware will reject any registers that are not allowed (Demand registers were added in firmware V2.3.0 which are now allowed but if you attempted to program those registers into earlier firmware, the firmware would reject the changes).
In order to add THD parameters, you would need to have new firmware created which would allow those registers to be selected.