Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Posted: 2018-04-04 05:46 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
4 incoming connections, the Modbus Master is an outgoing one (allowing the 8600 to communicate to another device via Modbus TCP).
Link copied. Please paste this link to share this article on your social media post.
8600 only supports a maximum of 4 connected simultaneous sockets (total across all protocols).
Here is a summary of the available sockets per ION device.
Telnet will always disconnect the last connected socket if the maximum number of sockets are already in use.
Posted: 2018-04-04 10:21 AM
Link copied. Please paste this link to share this article on your social media post.
perfect,
after I saw in the manual that the fifth connection is dedicated to the master modbus
Thank you.