Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Posted: 2018-04-04 05:46 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
4 incoming connections, the Modbus Master is an outgoing one (allowing the 8600 to communicate to another device via Modbus TCP).
Link copied. Please paste this link to share this article on your social media post.
8600 only supports a maximum of 4 connected simultaneous sockets (total across all protocols).
Here is a summary of the available sockets per ION device.
Telnet will always disconnect the last connected socket if the maximum number of sockets are already in use.
Posted: 2018-04-04 10:21 AM
Link copied. Please paste this link to share this article on your social media post.
perfect,
after I saw in the manual that the fifth connection is dedicated to the master modbus

Thank you.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.