New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Daisy chaining four terminal RS-485 meters with single twisted twin (shielded) conductors eg. Beldin 9841
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2019-08-0104:39 PM
Daisy chaining four terminal RS-485 meters with single twisted twin (shielded) conductors eg. Beldin 9841
Hi,
Recently I learnt that meters with four RS-485 terminals can form a serial string with meters that have three RS-485 terminals using Beldin 9841 or equivalent cables:
Where only Schneider meters with four RS-485 terminals exist in a serial string, what is the advantage of specifying Beldin 9842 over Beldin 9841 cables?
Would wiring a single shielded twisted pair to the D0 (-) and D1 (+), and the shield wire to the 0V (RS-485) terminal of such meters, leaving the shield terminal vacant, compromise performance in any way?
Link copied. Please paste this link to share this article on your social media post.
2019-08-0209:54 AM
Would wiring a single shielded twisted pair to the D0 (-) and D1 (+), and the shield wire to the 0V (RS-485) terminal of such meters, leaving the shield terminal vacant, compromise performance in any way?
Possibly, while the shield in 4 wire connections is not connected in the meter, it does help to isolate interference. In an environment with electromagnetic interference you will see a difference in performance between the 2 configurations.
Link copied. Please paste this link to share this article on your social media post.
2019-08-0209:54 AM
Would wiring a single shielded twisted pair to the D0 (-) and D1 (+), and the shield wire to the 0V (RS-485) terminal of such meters, leaving the shield terminal vacant, compromise performance in any way?
Possibly, while the shield in 4 wire connections is not connected in the meter, it does help to isolate interference. In an environment with electromagnetic interference you will see a difference in performance between the 2 configurations.