DNP3?
Have been familiar with ION, BACnet, Lon and Modbus. Newer kid in town DNP3. Are we seeing this implemented by SCADA and / or BMS/BAS people?
Reply
Reply 1
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
2016-04-02
11:07 AM
Michael, can't believe no one responded on this. DNP 3.0 is primarily used by utilities in North America. You would not see it used very often outside of the utilities. It is used for meters. relays reclosers etc to talk to the utility SCADA systems.