Question Synchronising ION7650 using GPS ASCII string

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Question Synchronising ION7650 using GPS ASCII string
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
sesa288596
sesa288596
Cadet

Posted: ‎2015-06-06 03:02 PM . Last Modified: ‎2020-04-22 01:25 AM

0 Likes
2
714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-06-06 03:02 PM

Question Synchronising ION7650 using GPS ASCII string

Hello

I am trying to connect Arbiter GPS to ION meter, synchronising it with ASCII commands.

The meter configuration is the following:

COM 2 Protocol

GPS: Arbiter-Vorne

9600 baud

0.010 tran delay

102 unit id

8n1 serial

RS485 Bias ON

Clock Setup

Sync Source COM2

Sync Type UTC

Clock Source COMM

 

With this configuration ION is still unable to get synchronous. COM2 RX LED is On, so I am sure that the connection is good. I have also verified that the GPS is sending the right ASCII string:

 

44003533

55000

1199

 

Please check my procedure and comment in case I did something wrong.

 

Thanks for your advice.

Isaac

Labels
  • Labels:
  • ION Setup
Tags (2)
  • Tags:
  • ion
  • setup
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Anonymous user
Not applicable

Posted: ‎2015-10-08 07:37 AM

1 Like
0
651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-08 07:37 AM

Hello Isaac,

I see that no one has replied yet, so I would like to try to help.  I am with Cyber Sciences, and we make a Sequence of Events Recorder that can also output the ASCII time protocol used by the ION7650 (and 7550 and PM8000).  I know in this case you already have an Arbiter clock, but perhaps our experience can still help.  (Subject to confirmation by ION meter experts!)

1) You may want to set the Arbiter clock and ION meter (both devices) to use the ASCII option called "TIME + QUALITY" (instead of Arbiter:Vorne).  Vorne is a maker of large displays, and so that option is really best for that company's products.  Using the QUALITY choice will also be compatible with any HMI which displays time quality.

2) I don't think you should enable the RS485 BIAS (leave "off").  This is normally used to bias the master side of an RS485 network.  In this case, the Arbiter clock is master and ION meter the slave.

3) You listed all the ION meter details, but not the settings for the Arbiter clock.  You may want to double check that the clock is set exactly to match ION.

I hope something in this reply is helpful!

Reply
Yut
Captain Yut
Captain

Posted: ‎2016-04-05 12:45 AM

0 Likes
0
651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-04-05 12:45 AM

Quite an old question anyway I will try to solve.

I notice that COM2 was set as receiving port so the bias for RS-485 should be OFF ON is for the case that COM2 is use as Modbus Master. This is my analysis try it.

See if the event log show that time change occur or not.

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of