Control power PM5000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Control power PM5000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
502
Ramasamy_N
Captain Ramasamy_N Captain
115
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
106
Robert_Lee
Admiral Robert_Lee Admiral
94
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
p_dejarmy_encos
Lieutenant p_dejarmy_encos
Lieutenant

Posted: ‎2025-08-05 09:49 PM

0 Likes
1
69
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-05 09:49 PM

Control power PM5000

Hello,

 

We're installing several (+20) PM5340 meters in one enclosure, and we wish to account for the power drawn by the meters. The installation guides states that the meter has an AC burden of 5 W/11 VA at 415 Vac 

 

p_dejarmy_encos_0-1754455223294.png

 

So, i have some questions:

 

  1. If the Aux power is 120 Vac rather than 415 Vac, does the burden change or is it the same?
  2. Why is so much difference in W and VA? Is it a power factor thing?
  3. What number would be best for the aux power supply calculation for the enclosure?
  4. Why is the DC burden smaller than the AC burden?

 

Thanks in advance,

 

 

Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-08-06 07:31 AM . Last Modified: ‎2025-08-06 07:36 AM

3 Likes
0
54
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-06 07:31 AM

Hi @p_dejarmy_encos

 

  1. Burden at 120 Vac vs. 415 Vac:
    The wattage (5 W) remains nearly constant regardless of voltage, but VA (11 VA at 415 V) depends on voltage. At 120 V, the meter draws more current to maintain the same power, so VA will be lower, but current higher.

  2. Difference between W and VA:
    Yes, this is due to power factor. Watts (W) measure actual energy used, while Volt-Amps (VA) include both real and reactive power. A low power factor means the meter draws more apparent power than it actually consumes.

  3. Aux power supply sizing:
    Use VA for sizing to ensure the supply can handle the total load. For 20 meters:
    20×11 VA=220 VA
    You can also add margin e.g. 30% → 300 VA-rated supply is recommended for safe operation and future expansion.

  4. DC burden is lower than AC:
    DC power is more efficient for electronic devices — no need for AC-to-DC conversion, so less internal loss. That’s why the DC burden is 4 W, compared to 5 W for AC.

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Reply 1
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-08-06 07:31 AM . Last Modified: ‎2025-08-06 07:36 AM

3 Likes
0
55
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-06 07:31 AM

Hi @p_dejarmy_encos

 

  1. Burden at 120 Vac vs. 415 Vac:
    The wattage (5 W) remains nearly constant regardless of voltage, but VA (11 VA at 415 V) depends on voltage. At 120 V, the meter draws more current to maintain the same power, so VA will be lower, but current higher.

  2. Difference between W and VA:
    Yes, this is due to power factor. Watts (W) measure actual energy used, while Volt-Amps (VA) include both real and reactive power. A low power factor means the meter draws more apparent power than it actually consumes.

  3. Aux power supply sizing:
    Use VA for sizing to ensure the supply can handle the total load. For 20 meters:
    20×11 VA=220 VA
    You can also add margin e.g. 30% → 300 VA-rated supply is recommended for safe operation and future expansion.

  4. DC burden is lower than AC:
    DC power is more efficient for electronic devices — no need for AC-to-DC conversion, so less internal loss. That’s why the DC burden is 4 W, compared to 5 W for AC.

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of