Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Connect ION 8650 via serial port to PME

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Connect ION 8650 via serial port to PME
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
PowerLogic
PowerLogic ION8650 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
lsubillaga
lsubillaga
Explorer

Posted: ‎2023-10-19 02:54 PM

0 Likes
9
6439
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-19 02:54 PM

Connect ION 8650 via serial port to PME

Hello to everyone,

 

I have a case of two meters ION 8650 that are having communications troubles with the Ethernet port. The two devices are connected to different ports of the same unmanaged switch. The problem of the meters is that they have intermittent and random communication issues. They stop communicating via Ethernet port to a SCADA and to PME, also they don't respond to ping, even when the port on the switch seems to be on.

 

With this problem we are trying a different solution, that is connect the ION meter to SCADA (Modbus) and PME via serial port (COM4 - RS485). We are using a serial to Ethernet converter (Gateway). The Modbus protocol works fine so SCADA is going to work. The problem we have is with PME because we want to add the ION 8650 via Modbus protocol, but in PME it appears via ION protocol and we don't know how to change this. I don't know if there is a different procedure to add the ION via Modbus or what is the problem. 

 

Thank for your help, I wait for your comments. 

 

Regards

  • Thumbnail of PowerLogic ION8650 series
    PowerLogic
    PowerLogic ION8650 series
View products (1)
Labels
  • Labels:
  • ION8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-10-27 08:36 AM

0 Likes
2
6366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-27 08:36 AM

Hello @lsubillaga ,

 

You cannot have 1 comm port talk 2 protocols at the same time. The meter will support either ION or Modbus but NOT both at the same time. You cannot have PME and SCADA system use different ports. PME can have limited communications with Modbus and ION8650 meter. There is NO option that will get you want you want.

 

Do you have a support case regarding the Ethernet connection? Saying "we couldn't connect even ION Setup" does not tell me how you were connected to the meter at the time, via network or directly connecting computer to meter. Could the switch require 802.1x authentication (not supported on meter)? Could the meter have older connections that get "stuck" filling up the concurrent connection limit? Could the meter be in condition where it is trying to service a request from PME that is taking up CPU bandwidth causing meter to not respond to other packets. Does disconnecting meter from network for a minute return communications etc.

Not asking for all these questions to be answered on this forum but wanted to show why trying to troubleshoot this on a forum is not the best option. Recommend working with tech support to try and troubleshoot to understand that is happening. Perhaps they will want to get diagnostic information after comms restored to meter.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 9
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-10-20 12:45 PM

0 Likes
6
6420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-20 12:45 PM

Hello @lsubillaga ,

 

Regarding PME and ION8650 connected via modbus. PME only knows how to talk to ION meters with ION protocol. While is it possible to create a modbus device driver in PME for the PME8650, all you will get is real time data. Logged data, waveforms, event logs etc. will not be accessible via modbus in PME.

When meter is not accessible, are you able to Telnet/SSH to the meter?

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
lsubillaga
lsubillaga
Explorer

Posted: ‎2023-10-25 03:53 PM

0 Likes
5
6388
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-25 03:53 PM

Hello @Charles_Murison ,

 

No, we can't access the meter via Telnet/SSH. Is there another way to access the meter for a SCADA in Modbus and a PME? We only have port COM4 available because port COM1 is in use.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-10-26 01:17 PM

0 Likes
4
6379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-26 01:17 PM

Hello @lsubillaga ,

 

In PME you can create a DTE device driver and create a modbus driver that can talk to the ION8650 meter. Sadly this would not support onboard logs.

When meter does not respond, if you connect directly to the meter, does meter respond? Are you able to contact technical support to start a troubleshooting case.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Yut
Yut
Leader

Posted: ‎2023-10-27 01:11 AM

0 Likes
1
6376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-27 01:11 AM

Wonder when you have problem with ION8650 Ethernet port please check your Advance Ethernet setting see if all the port you need was set enabled are Yes. ION8650 work best with ION protocol no need to create Modbus map. At the same time SCADA can access via Modbus or DNP  via Ethernet port simultaneously. 

 

Yut_0-1698394136278.png

 

Reply
lsubillaga
lsubillaga
Explorer

Posted: ‎2023-10-27 07:06 AM

0 Likes
3
6372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-27 07:06 AM

Hello @Charles_Murison ,

 

When the meter does not respond we couldn't connect even ION Setup to it. In this case the main trouble is that we need the meter to be read by two systems: SCADA in Modbus protocol and PME via ION protocol to get all the available information from the meter. And we have only port COM4 available.

 

Regards,

Luis Subillaga

Falcon Ingenieria

Reply
lsubillaga
lsubillaga
Explorer

Posted: ‎2023-10-27 07:14 AM

0 Likes
0
6371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-27 07:14 AM

Hello @Yut ,

 

Actually the meter have Modbus TCP enabled, the meter works fine for some time but then, at a random moment it fails and communication doesn't get restored until the meter is rebooted manually.

 

Regards,

Luis Subillaga

Falcon Ingenieria

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-10-27 08:36 AM

0 Likes
2
6366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-27 08:36 AM

Hello @lsubillaga ,

 

You cannot have 1 comm port talk 2 protocols at the same time. The meter will support either ION or Modbus but NOT both at the same time. You cannot have PME and SCADA system use different ports. PME can have limited communications with Modbus and ION8650 meter. There is NO option that will get you want you want.

 

Do you have a support case regarding the Ethernet connection? Saying "we couldn't connect even ION Setup" does not tell me how you were connected to the meter at the time, via network or directly connecting computer to meter. Could the switch require 802.1x authentication (not supported on meter)? Could the meter have older connections that get "stuck" filling up the concurrent connection limit? Could the meter be in condition where it is trying to service a request from PME that is taking up CPU bandwidth causing meter to not respond to other packets. Does disconnecting meter from network for a minute return communications etc.

Not asking for all these questions to be answered on this forum but wanted to show why trying to troubleshoot this on a forum is not the best option. Recommend working with tech support to try and troubleshoot to understand that is happening. Perhaps they will want to get diagnostic information after comms restored to meter.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
lsubillaga
lsubillaga
Explorer

Posted: ‎2023-10-30 08:34 AM

0 Likes
1
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-30 08:34 AM

Hello @Charles_Murison ,

 

Yes, I think this problem should be analyzed by support tech, but they tell me to post the case in the forum first and then if it could not be solved in the forum they could help me. So I will contact them again and ask for help. Thank you for your help.

 

Regards,

Luis Subillaga

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-10-30 08:44 AM

0 Likes
0
6346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-30 08:44 AM

Hello @lsubillaga ,

 

Could you let me know who in tech support asked you to post on the forum first please.

 

Thank you,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore