Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Communication problems of 7550 and 8650 energy meters ION Setup

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Communication problems of 7550 and 8650 energy meters ION Setup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
danielbarrantes
danielbarrantes
Troubleshooter

Posted: ‎2021-09-07 12:08 PM

1 Like
4
4049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-07 12:08 PM

Communication problems of 7550 and 8650 energy meters ION Setup

Currently I do not have communication with 7550 and 8650 energy meters which are connected by ethernet. The curious thing is that the same meter can be interrogated from another site (it is interrogated by 2 different utilities) and also from a SCADA (Ingeteam).

 

The problem occurs only in the office called "Santa Cruz", so the decision was made to carry out a test by changing the energy meter for a computer with the same IP and the same gateway, which if it was possible to ping (unlike the meter).

Basic services have already been restarted, the server has been rebooted, ports 7700 and 502 have been opened, and the configuration has been reviewed in ION Setup, however, the ping is still not successful.

The Santa Cruz server is old and has windows server 2008.

 

I attach a screenshot where the ping tests and the server characteristics are observed.

 

Ping a 8650 (bueno) y 7550 (malo).PNGServer Santa Cruz.PNG

 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Yut
Yut
Leader

Posted: ‎2021-09-30 11:43 PM

0 Likes
0
3924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-30 11:43 PM

You may use tracert  192.168.190.100 to see where the packet stop in your network it might at some of the router.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 4
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-09-21 11:31 AM

1 Like
0
3986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 11:31 AM

Hello @danielbarrantes ,

 

If I am reading your screenshots correctly, the IP addresses of these meters is 192.168.X.X, these are classified as class C IP address which has very specific behaviors on Networks. I am not an IT expert but these would have to be very specific networking configured (Such as Virtual Lans, VLAN for short) to get the different sites to talk to these meters.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2021-09-28 11:37 AM

0 Likes
0
3944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-28 11:37 AM

I'd like to point out that Windows 2008 Server R2 has reach EOL on January 14, 2020 so it isn't going to be receiving any further security updates from Microsoft so you might want swap it out.

I would suggest going to that remote location with a more recent laptop and see if plugging into the same network switch allows ION Setup to function (you could also use Wireshark to confirm that network traffic is being properly routed).

I would also perform an IPCONFIG /all from the command line to see what the server IP settings are (in comparison to the device settings).

This looks to be some type of IT issue (network switch(s) doesn't have the port open) or some type of gateway configuration of some kind.

Tags (1)
  • Tags:
  • english
Reply
Yut
Yut
Leader

Posted: ‎2021-09-30 11:43 PM

0 Likes
0
3924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-30 11:43 PM

You may use tracert  192.168.190.100 to see where the packet stop in your network it might at some of the router.

Tags (1)
  • Tags:
  • english
Reply
galcaPsE
galcaPsE
Explorer

Posted: ‎2023-04-07 04:38 PM

0 Likes
0
3051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-07 04:38 PM

Hi @danielbarrantes,

This is a typical networking issue, some tips:

- You will have the network diagram LAN/WAN to better understand your OT/IT network, for cybersecurity "don't share".

- Verified the physical layer connection, I noticed you do it.

- In the server use command prompt console and type "tracert 192.168.190.XX" it's very useful. Test with "tracert" in the same LAN (192.168.190.XX) 1 meter in OK condition and the other's 2 meter's (IP 100 and 106) with problems.

- You mentioned office "Santa Cruz" and I think used IT gateway for this purpose. In some cases IT deparment i) put new rules on firewall's, ii) change some logical topology on gateway or iii) have a "real physical problem" in other IT gateway which is the route for the LAN "Prime Server".

 

- It's recommended you have "a picture or baseline" of the protocols in your LAN, wireshark is a powerful tool for this purpose.

- If you solved the problem, install your laptop in the same LAN of Server, them use a tool like "RuggedPing" or "Angry IP Scanner" for discover the LAN 192.168.X.Y. only a few seconds to verify your IP's management.

 

Regards,

 

    

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore