Dear SE Support/ SE Expert
I require a support solution for changing the power supply board of the ION 8650 from auxiliary power (high voltage) to a standard power supply (blade-powered/self-supply).
We need to utilize the 110V AC from the PT signal for self-supply to replace the Jemstar meter with the ION8650 meter.
Thank you very much.
Best Regard,
Lerson T.
lerson@thaioilgroup.com
Link copied. Please paste this link to share this article on your social media post.
Hello @arttop ,
This change cannot be done in the field. The meter needs to be returned to the factory and the changes done there. I recommend working with your sales channels to get RMA to have the meter's power supply changed.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @arttop ,
This change cannot be done in the field. The meter needs to be returned to the factory and the changes done there. I recommend working with your sales channels to get RMA to have the meter's power supply changed.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Dear Charles_Murison
I followed your recommendations and thank you for your advice.
Best Regard,
Lerson T.