Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82563members
350181posts

Cannot open PM5560 webpage

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Miyai
Ensign
Ensign
0 Likes
2
231

Cannot open PM5560 webpage

Hello,

 

How do I unlock the PM5560 webpage after 5 or more failed login attempts?

 

I updated the firmware of PM5560 from 2.8.3 to 4.1.8, but I am having trouble opening the webpage.

locked.jpg

 

Best regards,

Miyai

Tags (1)

Accepted Solutions
Romain_Polette
Sisko Sisko
Sisko

Re: Cannot open PM5560 webpage

Hi @Miyai , 

With the latest FW version, the USER1 / PASS1 credentials are no more valid.

 

Please check here:

https://www.productinfo.schneider-electric.com/pm5500/595e2aa946e0fb0001f715da/PM5500%20user%20manua...

 

Regards, 

 

Romain POLETTE - Global Expert Technical Support - Digital Power Division
38EQI - Eybens - France

See Answer In Context

Tags (1)
2 Replies 2
Romain_Polette
Sisko Sisko
Sisko

Re: Cannot open PM5560 webpage

Hi @Miyai , 

With the latest FW version, the USER1 / PASS1 credentials are no more valid.

 

Please check here:

https://www.productinfo.schneider-electric.com/pm5500/595e2aa946e0fb0001f715da/PM5500%20user%20manua...

 

Regards, 

 

Romain POLETTE - Global Expert Technical Support - Digital Power Division
38EQI - Eybens - France
Tags (1)
Miyai
Ensign
Ensign
0 Likes
0
199

Re: Cannot open PM5560 webpage

Hi @Romain_Polette 

 

I was able to login.

Thank you for advise.

 

 

Best regards,

Miyai

Tags (1)