Can you have a Sag/Swell Alarm on a PM8 trigger a pulse or close an output to notify another system an event has occurred?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: Can you have a Sag/Swell Alarm on a PM8 trigger a pulse or close an output to notify another system an event has occurred...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
521
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
135
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
sesa73127
sesa73127 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-02-19 09:36 AM

0 Likes
2
1222
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-19 09:36 AM

Can you have a Sag/Swell Alarm on a PM8 trigger a pulse or close an output to notify another system an event has occurred?

We have some PM8's that the customer wants to be informed of when a Sag/Swell Event has occurred.  They don't have any Software, so they were wondering if a Sag/Swell Alarm could trigger an output pulse or close the contact on the standard KYZ output build into the PM8s

Thanks

Tags (8)
  • Tags:
  • alarm
  • alarming
  • event
  • kyz
  • pm8
  • sag
  • swell
  • trigger
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2014-02-19 05:07 PM

0 Likes
0
1171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-19 05:07 PM

According to the user manual (http://www.naic.edu/~phil/hardware/manuals/PM800UserGuide.pdf) on page 67 it states

Operate any output relays when the event is detected.

It appears that the PM870 may be the only device that will allow you to do a pure Sag/Swell detection for an alarm condition as per the IONSetup Device Configuration Guide Page 39 (http://www.powerlogic.com/literature/ION_Setup_Device_Configuration_Guide_70002-0293-03.pdf)

Incidentally Page 37 of the guide linked above mentiosn how to configure an alarm to use relays. (point 11)

11. If you want to trigger a digital output or relay on an alarm, click the

Output button, select one of the available outputs, then click the button to move it to

the “Selected”column. Click OK

If you do not have a PM870 I tink you could just set an undervoltage alarm which is explained starting on page 37.

Don't forget to mark any responses you  get as eithe helpful or correct

See Answer In Context

Reply
Replies 2
Anonymous user
Not applicable

Posted: ‎2014-02-19 05:07 PM

0 Likes
0
1172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-19 05:07 PM

According to the user manual (http://www.naic.edu/~phil/hardware/manuals/PM800UserGuide.pdf) on page 67 it states

Operate any output relays when the event is detected.

It appears that the PM870 may be the only device that will allow you to do a pure Sag/Swell detection for an alarm condition as per the IONSetup Device Configuration Guide Page 39 (http://www.powerlogic.com/literature/ION_Setup_Device_Configuration_Guide_70002-0293-03.pdf)

Incidentally Page 37 of the guide linked above mentiosn how to configure an alarm to use relays. (point 11)

11. If you want to trigger a digital output or relay on an alarm, click the

Output button, select one of the available outputs, then click the button to move it to

the “Selected”column. Click OK

If you do not have a PM870 I tink you could just set an undervoltage alarm which is explained starting on page 37.

Don't forget to mark any responses you  get as eithe helpful or correct

Reply
sesa73127
sesa73127 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-02-20 03:08 PM

0 Likes
0
1171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-20 03:08 PM

I did read the PM8 user guide, but it wasn't too clear on how I needed to do this.  The ION setup definitely sets my mind at ease that this is possible.  Thank you!

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore