Is the Power factor sign convention Chart wrong in PM800 user manual

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Is the Power factor sign convention Chart wrong in PM800 user manual
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
sesa207393_brid
Ensign sesa207393_brid Ensign
Ensign

Posted: ‎2013-11-29 05:04 AM

1 Like
2
1045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-11-29 05:04 AM

Is the Power factor sign convention Chart wrong in PM800 user manual

Hello everyone,

In the Power factor sign convention chart for PM800, it shows that in quadrant 2, the load is capacitive and the load in quadrant 3 is inductive. But I think it's wrong, because there are different explain in the user manual of PM5350 and IEEE1459. Can anybody help to confirm whether it's right? Thank you!

2795

The PQS Coordinate System chart in PM5350 user guide: in Quad2 the load is inductive and in Quad3 it's capacitive load.

2796

Four quadrant power flow directions chart is IEEE1459-2000:

2797

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2014-02-20 10:18 AM

0 Likes
0
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-20 10:18 AM

The information in the PM800 series user guide is correct.  Some information in the PM5350 user guide is a bit confusing, so we tried to improve the description in the PM5000 series tech docs.

PM5500 series user manual has a section that describes power factor and how it is stored in the meter's Modbus register (Chapter 16: Power, energy and power factor).

31493150

See Answer In Context

Reply
Replies 2
DanL
Captain DanL Captain
Captain

Posted: ‎2014-01-16 01:42 PM

1 Like
0
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-01-16 01:42 PM

In general there is consensus on how to describe a system with net positive real (active) power flow.

It is less clear how to describe a system in which the "load" current exceeds 90 degrees from the supply voltage (such as power generation).

https://www.msl.irl.cri.nz/sites/all/files/training-manuals/TG28%20Mar%202013.pdf

IEEE 1459 (both 2000 and 2010) has no direct discussion on the description nor definition of the terms Lead, Lag, Inductive Load, Capacitive Load - especially in regards to quadrants 2 and 3. However, a primary contributer to IEEE 1459 has indicated that some of his underlying assumptions about negative power were incorrect and that another revision is needed to correct this.

http://powerstandards.com/Shymanski/draft.pdf

The PM800 documentation agrees with other standards and references in the designation of capacitive/inductive and lead/lag:

see IEC62053-23, IEC62053-24, IEC61557-12, IEC61268,

and

Page 243 of Handbook For Electricity Metering 10th Ed.

2979

The simple validation test that makes sense to me is where a power meter is monitoring an inductive motor load:

Wired correctly to measure power delivered to the load as positive, the load will be in Q1 (lagging/inductive).

Wired with the current sensor backwards, to measure power delivered to the load as negative, the same "load" will be in Q3 (lagging/inductive).

The PM800 supports two conventions for PF sign: "IEEE" and "IEC"

The convention called "IEEE" appears a little misleading to me in that the current IEEE definitions for signing PF all agree with the IEC definitions - the sign of PF is the same as the sign of the active power flow. In any case, the intent of this configuration is to use the sign of the PF register to directly indicate lead (capacitive) vs. lag (inductive) to the user.

The PM5350 manual appears to be derived from the superset of the IEC diagram and the (uncorrected) IEEE1459 diagram.

From some quick testing done here, the PM5350 device does not appear to have indicators or registers for neither
Leading/Lagging nor Inductive/Capacitive.

The plan is to revise the PM5350 documentation.

Dan Loewen

Reply
Anonymous user
Not applicable

Posted: ‎2014-02-20 10:18 AM

0 Likes
0
934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-20 10:18 AM

The information in the PM800 series user guide is correct.  Some information in the PM5350 user guide is a bit confusing, so we tried to improve the description in the PM5000 series tech docs.

PM5500 series user manual has a section that describes power factor and how it is stored in the meter's Modbus register (Chapter 16: Power, energy and power factor).

31493150

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of