Can you have a Sag/Swell Alarm on a PM8 trigger a pulse or close an output to notify another system an event has occurred?

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
sesa73127
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
2
278

Can you have a Sag/Swell Alarm on a PM8 trigger a pulse or close an output to notify another system an event has occurred?

We have some PM8's that the customer wants to be informed of when a Sag/Swell Event has occurred.  They don't have any Software, so they were wondering if a Sag/Swell Alarm could trigger an output pulse or close the contact on the standard KYZ output build into the PM8s

Thanks


Accepted Solutions
BrianB
Lieutenant Lieutenant
Lieutenant
0 Likes
0
227

Re: Can you have a Sag/Swell Alarm on a PM8 trigger a pulse or close an output to notify another system an event has occurred?

According to the user manual (http://www.naic.edu/~phil/hardware/manuals/PM800UserGuide.pdf) on page 67 it states

Operate any output relays when the event is detected.

It appears that the PM870 may be the only device that will allow you to do a pure Sag/Swell detection for an alarm condition as per the IONSetup Device Configuration Guide Page 39 (http://www.powerlogic.com/literature/ION_Setup_Device_Configuration_Guide_70002-0293-03.pdf)

Incidentally Page 37 of the guide linked above mentiosn how to configure an alarm to use relays. (point 11)

11. If you want to trigger a digital output or relay on an alarm, click the

Output button, select one of the available outputs, then click the button to move it to

the “Selected”column. Click OK

If you do not have a PM870 I tink you could just set an undervoltage alarm which is explained starting on page 37.

Don't forget to mark any responses you  get as eithe helpful or correct

See Answer In Context

2 Replies 2
BrianB
Lieutenant Lieutenant
Lieutenant
0 Likes
0
228

Re: Can you have a Sag/Swell Alarm on a PM8 trigger a pulse or close an output to notify another system an event has occurred?

According to the user manual (http://www.naic.edu/~phil/hardware/manuals/PM800UserGuide.pdf) on page 67 it states

Operate any output relays when the event is detected.

It appears that the PM870 may be the only device that will allow you to do a pure Sag/Swell detection for an alarm condition as per the IONSetup Device Configuration Guide Page 39 (http://www.powerlogic.com/literature/ION_Setup_Device_Configuration_Guide_70002-0293-03.pdf)

Incidentally Page 37 of the guide linked above mentiosn how to configure an alarm to use relays. (point 11)

11. If you want to trigger a digital output or relay on an alarm, click the

Output button, select one of the available outputs, then click the button to move it to

the “Selected”column. Click OK

If you do not have a PM870 I tink you could just set an undervoltage alarm which is explained starting on page 37.

Don't forget to mark any responses you  get as eithe helpful or correct

sesa73127
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
227

Re: Can you have a Sag/Swell Alarm on a PM8 trigger a pulse or close an output to notify another system an event has occurred?

I did read the PM8 user guide, but it wasn't too clear on how I needed to do this.  The ION setup definitely sets my mind at ease that this is possible.  Thank you!