Can we extract the Zero Sequence Unbalance Factor (ZSUF) from an ION8650 power meter (or any PQ meter for that matter)?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Can we extract the Zero Sequence Unbalance Factor (ZSUF) from an ION8650 power meter (or any PQ meter for that matter)?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
sesa360183_brid
sesa360183_brid Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-02-10 02:13 AM

0 Likes
4
1286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-10 02:13 AM

Can we extract the Zero Sequence Unbalance Factor (ZSUF) from an ION8650 power meter (or any PQ meter for that matter)?

ZSUF = zero sequence components of voltages / positive sequence components of voltages

Maybe via VIP, ION configuration, or some register I have to look for?

This is a customer requirement. The customer requires Negative Sequence Unbalance Factor (NSUF) and ZSUF. As I checked in SE references, the voltage unbalance measurement that is used and displayed by our PQ meters is the NSUF. Now, I just need the ZSUF to fully comply with the requirement.

Any assistance/insight will help. Thank you very much!

Tags (6)
  • Tags:
  • ion8650
  • power quality
  • pq
  • unbalance
  • voltage unbalance
  • zsuf
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa56307_bridg
Lieutenant JG sesa56307_bridg Lieutenant JG
Lieutenant JG

Posted: ‎2016-02-10 10:48 AM

1 Like
1
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-10 10:48 AM

If I understand correctly, ZSUF and NSUF are the same as the supply voltage unbalance parameters defined in the IEC 61000-4-30 power quality standard, which states:

"u0 = (U0 / U1) * 100% = (zero sequence / positive sequence) * 100%"

"u2 = (U2 / U1) * 100% = (negative sequence / positive sequence) * 100%"

The ION8650A does measure these values according to the requirements of IEC 61000-4-30.  I believe the meter provides these measurements as 3-second values, 10-minute values, and 2-hour values as per the aggregation requirements of IEC 61000-4-30.  The historical values should be logged in ION data recorders named "4-30 2hr Log" and "4-30 10m Log", as well as "4-30 3s Log" which is disabled by default.  If you are looking for the measurements themselves, they are calculated in the default ION framework on two ION Arithmetic modules named "Sequence Comp1" and "Sequence Comp2" as follows:

"Sequence Comp1" module has output registers for "NegSeqComp 3s", "ZeroSeqComp 3s", NegSeqComp 10m", "ZeroSeqComp 10m"

"Sequence Comp2" module has output registers for "NegSeqComp 2hr", "ZeroSeqComp 2hr"

I hope this helps.  It does seem to be aligned with your description of ZSUF and NSUF.  There may be other ways of getting at this data in your system (e.g. 4-30 report in PME), but the meter certainly does calculate the values you describe.

Best regards,

David Tuckey, Firmware Architect

See Answer In Context

Reply
Replies 4
sesa56307_bridg
Lieutenant JG sesa56307_bridg Lieutenant JG
Lieutenant JG

Posted: ‎2016-02-10 10:48 AM

1 Like
1
1194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-10 10:48 AM

If I understand correctly, ZSUF and NSUF are the same as the supply voltage unbalance parameters defined in the IEC 61000-4-30 power quality standard, which states:

"u0 = (U0 / U1) * 100% = (zero sequence / positive sequence) * 100%"

"u2 = (U2 / U1) * 100% = (negative sequence / positive sequence) * 100%"

The ION8650A does measure these values according to the requirements of IEC 61000-4-30.  I believe the meter provides these measurements as 3-second values, 10-minute values, and 2-hour values as per the aggregation requirements of IEC 61000-4-30.  The historical values should be logged in ION data recorders named "4-30 2hr Log" and "4-30 10m Log", as well as "4-30 3s Log" which is disabled by default.  If you are looking for the measurements themselves, they are calculated in the default ION framework on two ION Arithmetic modules named "Sequence Comp1" and "Sequence Comp2" as follows:

"Sequence Comp1" module has output registers for "NegSeqComp 3s", "ZeroSeqComp 3s", NegSeqComp 10m", "ZeroSeqComp 10m"

"Sequence Comp2" module has output registers for "NegSeqComp 2hr", "ZeroSeqComp 2hr"

I hope this helps.  It does seem to be aligned with your description of ZSUF and NSUF.  There may be other ways of getting at this data in your system (e.g. 4-30 report in PME), but the meter certainly does calculate the values you describe.

Best regards,

David Tuckey, Firmware Architect

Reply
Yut
Captain Yut
Captain

Posted: ‎2016-02-10 07:53 PM

1 Like
1
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-10 07:53 PM

Please open Designer then take a look at IEC 61000-4-30 Power Quality Framework see the two Arithmetic Modules, Sequence Comp1 and Sequence Comp2 you have two choices of calculation.

I recommend everyone who will work with the PQ study the framework thoroughly there are many thing more than the document.

Reply
sesa360183_brid
sesa360183_brid Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-02-10 10:57 PM

0 Likes
0
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-10 10:57 PM

Thank you very much, David, for the detailed response!

Will try this solution when I go back to the site.

Reply
sesa360183_brid
sesa360183_brid Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-02-10 10:58 PM

0 Likes
0
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-10 10:58 PM

Will definitely consider this, Yut. This is very much in line with David's answer above as well! Thank you very much!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now