Hello everyone,
I could help with this problem that I have ?; I want to configure a ION8650B COM4 meter so you can communicate with the communication protocol DNP3.0 but shower at the time of configuration I get this error?
Deputy screenshots taken from the error.
http://www.mediafire.com/view/63j20qas0656e15/Meter_Configuration_Report_for_MW-1406A170-01.txt
http://www.mediafire.com/download/3b3hdvq50ckag94/Error+ION8650.docx
Thank You
Miguel Huaccha
Posted: 2015-07-06 03:59 PM
Link copied. Please paste this link to share this article on your social media post.
Hi Miguel,
You have to configure the "3rd Party Protocol" for this meter via ION Setup.
In DNP3.0 option you have to set up "Connection #1" to "Communicaction port 4 (DNP V3.00)"
Best Regards
Farid
Posted: 2015-07-06 03:59 PM
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of