Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2015-07-0602:30 PM
COM4 configuration error ION8650
Hello everyone,
I could help with this problem that I have ?; I want to configure a ION8650B COM4 meter so you can communicate with the communication protocol DNP3.0 but shower at the time of configuration I get this error?