COM4 configuration error ION8650

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Miguel_Huaccha
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

COM4 configuration error ION8650

Hello everyone,

I could help with this problem that I have ?; I want to configure a ION8650B COM4 meter so you can communicate with the communication protocol DNP3.0 but shower at the time of configuration I get this error?

Deputy screenshots taken from the error.

http://www.mediafire.com/view/63j20qas0656e15/Meter_Configuration_Report_for_MW-1406A170-01.txt

http://www.mediafire.com/download/3b3hdvq50ckag94/Error+ION8650.docx

Thank You

Miguel Huaccha


Accepted Solutions
Victor_Yacu
Lieutenant JG
Lieutenant JG

Re: COM4 configuration error ION8650

Hi Miguel,

You have to configure the "3rd Party Protocol" for this meter via ION Setup.

6965

In DNP3.0 option you have to set up "Connection #1" to "Communicaction port 4 (DNP V3.00)"

6966

Best Regards

Farid

See Answer In Context

1 Reply 1
Victor_Yacu
Lieutenant JG
Lieutenant JG

Re: COM4 configuration error ION8650

Hi Miguel,

You have to configure the "3rd Party Protocol" for this meter via ION Setup.

6965

In DNP3.0 option you have to set up "Connection #1" to "Communicaction port 4 (DNP V3.00)"

6966

Best Regards

Farid